Sizing cables from TX to LV Panel

Hi all,

Is it a common occurrence for ICPs/DNOs to not consider grouping factors when sizing supply conductors (TX to LV panel)? 

To my understanding, if the supply circuit fell within the scope of BS 7671:2018, as per note 5 of Table 4C1 in Appendix 4, I’d assume that the applicable grouping factor for a circuit consisting of 3 single core cables per phase, installed direct in ground (hypothetical example), would be 0.70.

Thanks,

Bh

Parents
  • All the jobs I have done I have calculated the CSA of the AWAs from the panel to the Tx and the LV contractor installs them and presents them to the DNO for connection.

    See my adjacent post on CT chambers.

    JP

Reply
  • All the jobs I have done I have calculated the CSA of the AWAs from the panel to the Tx and the LV contractor installs them and presents them to the DNO for connection.

    See my adjacent post on CT chambers.

    JP