Sizing cables from TX to LV Panel

Hi all,

Is it a common occurrence for ICPs/DNOs to not consider grouping factors when sizing supply conductors (TX to LV panel)? 

To my understanding, if the supply circuit fell within the scope of BS 7671:2018, as per note 5 of Table 4C1 in Appendix 4, I’d assume that the applicable grouping factor for a circuit consisting of 3 single core cables per phase, installed direct in ground (hypothetical example), would be 0.70.

Thanks,

Bh

Parents
  • Hi all, thanks for your replies.

    Does the ERA 69-30 series provide more guidance on single core cables laid direct in ground? If it does, where can I purchase the ERA 69-30 series? Can't seem to find anything from a simple google search.

    Also, is there any other guidance or standards that cover the topic?

  • This Wiring Matters Article from 2021 points to https://www.edifgroup.com/publications (although that's not responding for me at the moment)

       - Andy.

  • Hi Andy,

    I've tried that link before and didn't work then either.

  • https://www.era.co.uk/ looks to be down as well (might well redirect to/from the same place).

    Maybe have to wait until people are back at their desks on Monday and then for someone to notice or put another coin the meter (presuming they're in business still).

       - Andy.

  • ERA Edif have been owned by RINA for a while https://www.rina.org/en/about-us/history , maybe the old domains are no longer active?

Reply Children
  • Hi both, still no luck. Not sure what I can do...

     - Bh.