Volt drop % - Private Supply Def

Good day everyone 

Public supply Volt drop 3% Lighting 5% Power.

Private supply Volt drop 5% Lighting 8% Power.

Define private supply?

Option 1 - HV public grid supply to privately owned transformer. Is LV supply private?

Option 2 - Main source of supply is from Privately owned source of generation such as PV, diesel/gas/nuclear generator?

Why is this not defined in BS7671?

Parents
  • Quite simpy, if you receive a supply at HV, and under certain other conditions according to ESQCR if you take a supply at LV, you will have a connection agreement that tells you what you should expect at the supply terminals, which will not necessarily be U0 + 10 % / - 6 % for a "standard" LV public supply.

    There's no way that BS 7671 could know what terms you have agreed with the supplier ... and therefore the standard can't be specific about this.

Reply
  • Quite simpy, if you receive a supply at HV, and under certain other conditions according to ESQCR if you take a supply at LV, you will have a connection agreement that tells you what you should expect at the supply terminals, which will not necessarily be U0 + 10 % / - 6 % for a "standard" LV public supply.

    There's no way that BS 7671 could know what terms you have agreed with the supplier ... and therefore the standard can't be specific about this.

Children