Good day everyone 

Public supply Volt drop 3% Lighting 5% Power.

Private supply Volt drop 5% Lighting 8% Power.

Define private supply?

Option 1 - HV public grid supply to privately owned transformer. Is LV supply private?

Option 2 - Main source of supply is from Privately owned source of generation such as PV, diesel/gas/nuclear generator?

Why is this not defined in BS7671?

Parents
  • Just a thought here. Is there any provision which specifies voltage drop at HV. Surely, if HV is low, Lv must also be low?

    No specific provision in BS 7671 ... and agreed, but transformers with tap-changers and AVC can be used to overcome that (or, in the LV system, autotransformers with tap-changers)

  • Think we are drifting away from the question. What is a private supply in terms of BS7671? Option  1 or Option 2?

  • Think we are drifting away from the question. What is a private supply in terms of BS7671? Option  1 or Option 2?

    Anything other than a "standard" ESQCR public LV supply is the answer. Not drifting, that was answered earlier, and the discussion progressed beyond it.

  • I have searched the web and found the definition of a private supply according to BS 7671. A private supply is a supply that comes from a source of energy other than a public electricity supply system, This definition is also in agreement with the one given in [Wikipedia], which references BS 7671:2018 as its source. However, I could not find the exact location of this definition in the BS 7671

  • So just for clarity, your answer is both Option 1 & Option 2 will be considered private supply?

  • I think there is some misunderstanding about my answer. I did not say that both Option 1 and Option 2 are private supplies. I said that only Option 2 is a private supply. Option 1 is not a private supply, because it still relies on the public electricity supply system at the HV level. The private transformer does not alter the source of energy, only the voltage level. Therefore, Option 1 is a public supply with a private transformer, not a private supply. 

Reply
  • I think there is some misunderstanding about my answer. I did not say that both Option 1 and Option 2 are private supplies. I said that only Option 2 is a private supply. Option 1 is not a private supply, because it still relies on the public electricity supply system at the HV level. The private transformer does not alter the source of energy, only the voltage level. Therefore, Option 1 is a public supply with a private transformer, not a private supply. 