Volt drop % - Private Supply Def
Good day everyone
Public supply Volt drop 3% Lighting 5% Power.
Private supply Volt drop 5% Lighting 8% Power.
Define private supply?
Option 1 - HV public grid supply to privately owned transformer. Is LV supply private?
Option 2 - Main source of supply is from Privately owned source of generation such as PV, diesel/gas/nuclear generator?
Why is this not defined in BS7671?
  • Think we are drifting away from the question. What is a private supply in terms of BS7671? Option  1 or Option 2?
    Anything other than a "standard" ESQCR public LV supply is the answer. Not drifting, that was answered earlier, and the discussion progressed beyond it.
  • I have searched the web and found the definition of a private supply according to BS 7671. A private supply is a supply that comes from a source of energy other than a public electricity supply system, This definition is also in agreement with the one given in [Wikipedia], which references BS 7671:2018 as its source. However, I could not find the exact location of this definition in the BS 7671
  • So just for clarity, your answer is both Option 1 & Option 2 will be considered private supply?
  • I think there is some misunderstanding about my answer. I did not say that both Option 1 and Option 2 are private supplies. I said that only Option 2 is a private supply. Option 1 is not a private supply, because it still relies on the public electricity supply system at the HV level. The private transformer does not alter the source of energy, only the voltage level. Therefore, Option 1 is a public supply with a private transformer, not a private supply.
  • It looks confusing in the chat. I actually replied to gkenyon. I understand what you are saying and thats what I thought. I'm also aware of the Internet definitions you quoted. I always thought the same as you. However a colleague said the same as Chris Pearson above. If you own the transformer you are able to adjust the tappings on the transformer to achieve peak efficiency on your volt drops. So I tend to agree with them. Just wish BS7671 was clear on this.
  • When we don’t have a clear answer, we call it a grey area. It’s like the weather in Manchester, always cloudy and uncertain. Joy
  • Sweat smile
    Yes, they could both be considered a private supply, although as I have said the over-riding factors are not really the drop within the installation, but conformity with Regulations 525.1 and 525.201.
  • I’d go with Graham’s final conclusion. My opinion has been changed
    Why? Part 2 of BS 7671 contains the definitions within that standard?
    Also, what does "Wikipedia" define as a "source of energy" ?
    Wikipedia cannot interpret standards for us, I'm afraid.
    I'm not sure it's there.
    If you take the diagrams in BS 7671 at face value, a transformer is a 'source of energy' which further supports the explanation I have given that a "private transformer" is a "private source of energy" - or, if you like, a private supply.