Emergency Lighting Standard
I have come across some 6ft LED EM fittings that have no indicator light to show it is charging. They are maintained fittings and when you disconnect the power a separate LED illuminates. You can’t tell them apart from the non EM fittings unless you disconnect the power.
Does the standard require the EM light to have LED indicator during normal use?
  • What kind of lighting is it?  eg
    Escape route lighting
    Open area emergency lighting
    High-risk task area lighting
    Standby lighting
  • I think the standard you need is  Particular requirements - Luminaires for emergency lighting (IEC 60598-2-22:2021)
    I do not have a current copy to hand here, but more generally I note that the sophistication  of LED indicators varies widely between makers.
    In some cases it is just a "mains on" indicator, always on when there is a mains supply,  in other cases there is electronics that checks the battery voltage has reached some level that indicates it is charged, and in others yet more complex still with a micro controller that monitors the battery internal resistance by periodically pulsing a load and looking at the droop (a baby DC version of the familiar  Zs test if you like) and these models seem able to indicate many fault states with flashing lights of different pulse patterns or colours.
    I am not sure of the minimum required by  standard,  but clearly in a bid to differentiate, various makers go  above and beyond with red lights, green lights and in one very annoying model a selection of beeps and chirps - none of which appear to be harmonised.
    I am not aware of a proper emergency light that does not have provision for some sort of 'on charge' indication, and it certainly was a thing in the older versions of the standards for fittings with the battery built in (but not all battery backed up lights are actually emergency lights -as note above.)
  • Not really sure as I as not the designer, probably escape route lighting. Does it make a difference?
  • On Emergency lighting completion certificates For small new installations up to 25 self-contained luminaires one of the tick boxes needs ticking to confirm that after the system has been tested, each luminaire charging indicator operates correctly.
  • turns out there are LED indicator lights. Just hard to see and behind the opaque diffuser. Thank you for all the replies