SPD required after EICR?

Hi, after completing an EICR, should the lack of an SPD on a perfectly otherwise adequate board be classed as C2 or C3?

Also are SPD's required for any new circuit or only required when changing a fuseboard or for any circumstances where the SPD would be required to further protect any vulnerable equipment?

Parents
  • As an EICR is to see if the installation is safe or not i don't see as it should be coded at all generally. In the report summary i always put it is a recommendation but don't code it as i don't see it as unsafe.

    Gary

Reply
  • As an EICR is to see if the installation is safe or not i don't see as it should be coded at all generally. In the report summary i always put it is a recommendation but don't code it as i don't see it as unsafe.

    Gary