Extractor fans that do not require a 3 amp fuse ?

Hi guys.  i am struggling to source a bathroom  extractor fan with a short spigot that doesn't require a 3 amp fuse. Most of them seem very long to what they used to be which is a right pain sometimes. I only have 90mm to play with for the spigot and the existing only has a 3 pole isolator but no fuse. It would be a nightmare to alter as all the wiring is at the light switch and there is no access from above to try and alter it.  I usually use Vortice as they don't require the fuse but can't find one with a short enough spigot. I seem to remember there was another brand that didn't but can't remember what it is if anyone knows ? The fan is for a shower room ceiling although it is out of zones due to height .

Cheers

Gary

  • Would a combined 3 pole isolator with integral fuseholder be of any use to you - swap out the existing one?

    www.toolstation.com/.../p19707

  • Thanks for the reply. I have managed to find something suitable.  A Greenwood Unity CV2GIP smart timer with humidistat if anyone else in the same boat.   cheers

  • a combined 3 pole isolator with integral fuseholder

    Would such a device comply with BS 7671? I'm guessing the fuse is in just one of the L poles, leaving the other protected by the upstream lighting MCB. By BS 7671 definitions, the 3A fuse, being an overcurrent protective device, creates a new circuit, so we now have two distinct circuits but both sharing the same neutral - a contravention of 314.4. Granted most of the physical reasons for not borrowing a neutral probably don't apply in this particular circumstance, but I think it would still be tricky to be able to sign off as compliant.

      - Andy.

  • It wouldn't isolate both lives as far as i can see. The switch live would still be on if the light was on even if the permanent live is off..

    Gary

  • No fans actually require a 3A fuse. Fuses etc. are to protect the cable.

    If you actually want a fan where the manufacturer does not wrongly tell you you need a fuse, then buy one in Europe.

  • Indeed, a B6 mcb will pop a lot sooner than a 3A fuse will.

  • Fuses etc. are to protect the cable.

    So what protects the internals of the appliance? What's to stop the manufacturer specifying that the installer provide something on the supply side instead of having an extra protective device internally? (as seems to be the case here, and appears to be permitted by the equipment standards)

    Indeed, a B6 mcb will pop a lot sooner than a 3A fuse will.

    Not if the fault current is limited (e.g. due to a short between turns of a motor winding) - at 5A or 6A for example the 3A fuse will go far sooner.

      - Andy.

  • So what protects the internals of the appliance?

    A device fitted internally by the manufacturer as they do when necessary.

    What's to stop the manufacturer specifying that the installer provide something on the supply side instead of having an extra protective device internally?

    Why should that be considered acceptable?

    Are you suggesting that, for example, fan manufacturers make their products less safe for the UK than they do for places where such fuses are not available and the item would be on a 16A circuit?

  • Are you suggesting that, for example, fan manufacturers make their products less safe for the UK than they do for places where such fuses are not available and the item would be on a 16A circuit?

    I'm not sure they do go on 16A circuits on the continent - the French diagrams I've seen always put them on a separate C2 MCB.

       - Andy.

  • The monsoon ipx5 by national ventilation is my go to in most cases , and has an internal 3a fuse on the circuit board .