I manage an old industrial complex built in 1960. During the EICR testing most of the fixed wiring circuits have failed the insulation tests, with readings of less than 1Mohm. These cables are all MICC and have been untouched since installation. To replace all these cables would be an epic task and these works would need to be done in the next three months to satisfy the handover of the premises to the landlord.

Is there a method to test these 'legacy' cables other than to test to current standards (500v)? Istr mention of testing such cables at 50v but I can't find where I saw this. Is there a method to implement mitigation measures instead of replacing all the cables, or spending many hours isolating sections to fault find?

As you may be able to tell, I'm no electrician and every contractor I've approached has insisted that the entire building needs to be recabled, which isn't currently viable.

Thanks.

Parents
  • I would be interested to hear how much experience with micc cable the tester as under the belt. 

    The idea the entire site needs rewiring sounds somewhat extreme as I have seen 'low' readings dealt with with a blowtorch and re-potting the end(s).

    Is that reading for the full board then transposed against each circuit on the schedule of test results? Do you have any previous EICR against the installation?