Legacy Installation EICR

Greetings all.

Hopefully this will be an easy one for the hive mind, and I've tried the 'Search' but to no avail:

I manage an old industrial complex built in 1960. During the EICR testing most of the fixed wiring circuits have failed the insulation tests, with readings of less than 1Mohm. These cables are all MICC and have been untouched since installation. To replace all these cables would be an epic task and these works would need to be done in the next three months to satisfy the handover of the premises to the landlord.

Is there a method to test these 'legacy' cables other than to test to current standards (500v)? Istr mention of testing such cables at 50v but I can't find where I saw this. Is there a method to implement mitigation measures instead of replacing all the cables, or spending many hours isolating sections to fault find?

As you may be able to tell, I'm no electrician and every contractor I've approached has insisted that the entire building needs to be recabled, which isn't currently viable.

Thanks.

Parents
  • I would think the landlord is responsible for the fixed wiring or am i missing something here ?

    Gary

  • Sounds more like an industrial let being vacated that has to be returned to the landlord 'as supplied' - which normally means for tenants taking out any thing you have added, maybe repainting and in some cases even dilapidation work - that is putting back in  older dated and even sometimes broken equipment and fittings  that were removed when you moved in - to return it exactly to the original condition.

    The laws of a badly worded contract can act in strange ways - usually common sense kicks in but not always.

    Mike.

  • A mapj1 says, it's a 25 year lease with a lease agreement to return the building at the end of the tenancy in a safe condition. I can't find any historic records to show what the readings were back in 1999 when the lease was signed. 

Reply
  • A mapj1 says, it's a 25 year lease with a lease agreement to return the building at the end of the tenancy in a safe condition. I can't find any historic records to show what the readings were back in 1999 when the lease was signed. 