EICR Coding for main isolating switch

What would the code be for an isolator switch of a distribution board not having any indication of its position(on or off)?

There are two distribution boards at the origin, one is off when down, the other is off when up. One isn't labelled or marked any way.

Also, would you code for no single point of isolation for the whole installation?

Parents
  • In my vie simply marking ON/OFF or 0 and 1 would be fine and I consider that regarding this as a  modification is over pedantic.

    Every installation needs a single point of isolation, but more than one installation is permitted in the same building. So no code needed for the two main switches.

  • As very few of the general public will have the iso guide to switch symbols to hand, in an English speaking environment, I'd strongly prefer the words "on" to indicate the on (alive) position and "off" for the off (dead) position. (I have no problem with ein / aus for Germans.. ).

    Why a completed circle should indicate a broken circuit has never been especially intuitive to me, and and allusions to binary are wonderful but in many systems I have seen the switches are actually wired as active low, open pull-up, as that  saves taking power to the front panel.
    Mike.

Reply
  • As very few of the general public will have the iso guide to switch symbols to hand, in an English speaking environment, I'd strongly prefer the words "on" to indicate the on (alive) position and "off" for the off (dead) position. (I have no problem with ein / aus for Germans.. ).

    Why a completed circle should indicate a broken circuit has never been especially intuitive to me, and and allusions to binary are wonderful but in many systems I have seen the switches are actually wired as active low, open pull-up, as that  saves taking power to the front panel.
    Mike.