AC & DC Cable segregation underground

Afternoon, 

I am currently reviewing a design that has 2 X low voltage DC 200KW circuits (185mm Ho7 Singles) run ducted underground at a depth of 600mm along with a couple of ducted 32A single phase circuits (25mm Ho7) (Both Band II circuits) the separation distance between all circuits underground is 0.25m is this ok in terms of AC / DC segregation? the AC circuit is a standard 230V circuit and the DC circuit can have a voltage of up to 1000V (EV Charger) 

using TABLE A444.1 – Summary of minimum separation distances where the specification and/or the intended application of the information technology cable is not available, shows a 200mm separation distance. but I wanted to make sure there was nothing I was missing, 

Thank you in advance 

Parents
  • TCrabbe,

    If this installation is on a fuel filling station, there are other documents to be complied with regarding installa nd location of d.c cabling. Im only mentioning this given the number of incorrect EVSE installs on fuel filling stations recently.

    If its not on a fuel filling station then, the others that have replied have given sound advice.

    Cheers GTB

Reply
  • TCrabbe,

    If this installation is on a fuel filling station, there are other documents to be complied with regarding installa nd location of d.c cabling. Im only mentioning this given the number of incorrect EVSE installs on fuel filling stations recently.

    If its not on a fuel filling station then, the others that have replied have given sound advice.

    Cheers GTB