An interesting design issues has cropped up. The DNO has provided a 100A TT supply. Would the fusing be different from the BS 1361 fusing for TNC-S arrangement? Also when designing downstream electrical designs I'm having difficulty with excessive energy let throughs. Load end RCBO's, upstream BS88-2 in combination with RCD (30mA). Any suggestions welcome

Parents
  • Fusing for L-N faults or shorts remains unchanged on TT relative to TN supplies. What differs (of course) is that the Zs is is  nearly always  too high to blow that fuse, or indeed any fuse at all  in many cases  so RCD/ earth fault relay protection at or near the origin is required.
    Can you clarify the problem of excessive energy let through ? usually TT is associated with the opposite problem  and fault currents that do not trouble 2.5mm let alone switchgear..

    What are  your measured Zs (with and without bonding in place) and your L-N loop PSSC ?

    regards Mike.

Reply
  • Fusing for L-N faults or shorts remains unchanged on TT relative to TN supplies. What differs (of course) is that the Zs is is  nearly always  too high to blow that fuse, or indeed any fuse at all  in many cases  so RCD/ earth fault relay protection at or near the origin is required.
    Can you clarify the problem of excessive energy let through ? usually TT is associated with the opposite problem  and fault currents that do not trouble 2.5mm let alone switchgear..

    What are  your measured Zs (with and without bonding in place) and your L-N loop PSSC ?

    regards Mike.