H07 for overhead supply cable

Looking at replacing an overhead supply cable, support by catenary wire 6m above ground on a farm now renting buildings out to small businesses.

Cable is supplying a small barn that will be used by a family to store and work on stock cars 

Current cable is T+E supported by catenary wire, it's been cut at both ends, unsuitable for outside use, therefore replacing it.

First thought was armoured cable, but then thinking that something like HO7-rn-f might be better. 

        No armoured and surface clipped, so no need for RCD protection on this submain

        Less weight and more flexible, 

Any reason not to use HO7-rn-f ?


Parents
  • Thanks all for the thoughts overall I agree that SWA is probably the better solution. I was looking at other options as it's a TT earth and from my quick look at a very messy incoming supply area I think there is a reasonable chance that non of the submains had RCD protection. There were 10 to 15 enclosures, most with metal lid's that I couldn't access easily on the initial visit. I didn't see anything that was obviously an RCD.

    Owner agrees it all needs rework, but wanted that as a future project, hence considering a sub main cable that I could use without RCD protection, but maybe the steel catenary means I need RCD protection anyway. Life would have been much easier if the customer hadn't cut the existing twin + earth, I would have been comfortable continuing to use it with a  comment on the certificate. Now whatever happens we are looking at having to get something like a HIAB in to enable replacement of the cable.

    Clearly need to go back to site to look a bit more closely at the incoming area and many other things.

  • if you have to hire a cherry picker to replace it you might be better abandoning the catenary and using split concentric which can self support over reasonable spans. There are a few threads on here that discuss the limitations of this cable but its lightweight and relatively inexpensive.  If you do go this way get a couple of preform wire 'dead ends' to support it.

  • Thanks for the idea. The span is in the region of 20 meters, don't see avoiding the catenary as an option.

  • 20m is quite a span unless the cable is quite chunky- what copper cross-section would you be looking at ?

    Mike

  • Not quite sure at the moment, trying to pin customer down on max demand. If the total cable run is 25m with 60 amps, looks like I can get away with a 10mm cable, which gives a 3.07% voltage drop. Clearly need to do some actual measurements on length of run. Given the number of other buildings running on a 100 amp single phase supply even this is pushing our luck with the main supply fuse.

Reply
  • Not quite sure at the moment, trying to pin customer down on max demand. If the total cable run is 25m with 60 amps, looks like I can get away with a 10mm cable, which gives a 3.07% voltage drop. Clearly need to do some actual measurements on length of run. Given the number of other buildings running on a 100 amp single phase supply even this is pushing our luck with the main supply fuse.