IDNO supply up the building i.e. Bemco boards then communal metering to consumer units within each apartment. Building has LPS.
Type 1 +2 surge protection has been installed to landlord common areas switchboard.
The IET is carrying out some important updates between 17-30 April and all of our websites will be view only. For more information, read this Announcement
IDNO supply up the building i.e. Bemco boards then communal metering to consumer units within each apartment. Building has LPS.
Type 1 +2 surge protection has been installed to landlord common areas switchboard.
What is the value of the nominal lightning impulse current (Iimp) per pole that you have chosen? If the building has a lightning protection system (LPS) or is within 50 m of a lightning conductor, a type 1 surge protection device (SPD) should be installed at the main switchboard. Then, a type 2 SPD should be installed at the distribution boards that are 10 m away from the main switchboard. Finally, a type 3 SPD should be installed at the sensitive equipment that requires further protection and is 10 m away from the distribution boards.
What is the value of the nominal lightning impulse current (Iimp) per pole that you have chosen? If the building has a lightning protection system (LPS) or is within 50 m of a lightning conductor, a type 1 surge protection device (SPD) should be installed at the main switchboard. Then, a type 2 SPD should be installed at the distribution boards that are 10 m away from the main switchboard. Finally, a type 3 SPD should be installed at the sensitive equipment that requires further protection and is 10 m away from the distribution boards.
We're making some changes behind the scenes to deliver a better experience for our members and customers. Posting and interactions are paused. Thank you for your patience and see you soon!
For more information, please read this announcement