Smoke Damper 230v actuators

So, regarding 230v actuators, would you terminate it in a switched fused spur or an unswitched fused spur?  

Parents
  • For me, it would be unfused. I would choose less overload and fault current protection. This is due to the risk of unexpected disconnection of the circuit, as stated in regulation 433.3.3 (v) and regulation 434.3

Reply
  • For me, it would be unfused. I would choose less overload and fault current protection. This is due to the risk of unexpected disconnection of the circuit, as stated in regulation 433.3.3 (v) and regulation 434.3