This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

33kV/11kV delta delta transformer

When specifying 33kV/11kV and 11kV/400V transformers for new building project is it acceptable for 33kV/11kV transformer to be specified with delta-delta windings thus relying on cable screen and ground earth paths back to the remote DNO main substation? As opposed to delta-star with earthed neutral star point.

Parents
  • If it's delta delta, how do you provide an earth reference to the secondary side?

       - Andy.

Reply
  • If it's delta delta, how do you provide an earth reference to the secondary side?

       - Andy.

Children
No Data