33kV/11kV delta delta transformer

When specifying 33kV/11kV and 11kV/400V transformers for new building project is it acceptable for 33kV/11kV transformer to be specified with delta-delta windings thus relying on cable screen and ground earth paths back to the remote DNO main substation? As opposed to delta-star with earthed neutral star point.

Parents Reply Children
  • Mike/Andy

    1. Thanks for the advice and references that is understood. I can now see need for creation of own earth using star transformation on secondary probably with neutral earthing resistor.