SWA Cable Gland Adapter Piece

Hello 

Can anyone offer some help regarding the use of  fabricated SWA cable gland adapter/extension pieces?

During installation works, our contractor has made off 2No 5C, 240mm2, SWA cables too short to reach the gland plate.

To avoid replacing the cables, they have site fabricated two "Extension pieces" from some 316 S/S to allow the cables to be terminated (shown below).

We have some reservations accepting the installation, therefore I am seeking some clarity on the following points:

  • Is this an acceptable installation method under BS7671?
  • What specific clauses in BS7671 would these pieces have to conform to (511.1?)
  • is there anything in the Regulations that would allow this installation to be rejected?

Thank you.

Parents
  • One more thought to add to the mix - what's the conductivity of 316 stainless steel like? (I've a feeling that SS is often poorer than plain steel, which in turn is poorer than brass or copper) so it might run a fair bit warmer under fault conditions than an equivalent conduit coupler for instance.

       - Andy.

Reply
  • One more thought to add to the mix - what's the conductivity of 316 stainless steel like? (I've a feeling that SS is often poorer than plain steel, which in turn is poorer than brass or copper) so it might run a fair bit warmer under fault conditions than an equivalent conduit coupler for instance.

       - Andy.