SWA Cable Gland Adapter Piece

Hello 

Can anyone offer some help regarding the use of  fabricated SWA cable gland adapter/extension pieces?

During installation works, our contractor has made off 2No 5C, 240mm2, SWA cables too short to reach the gland plate.

To avoid replacing the cables, they have site fabricated two "Extension pieces" from some 316 S/S to allow the cables to be terminated (shown below).

We have some reservations accepting the installation, therefore I am seeking some clarity on the following points:

  • Is this an acceptable installation method under BS7671?
  • What specific clauses in BS7671 would these pieces have to conform to (511.1?)
  • is there anything in the Regulations that would allow this installation to be rejected?

Thank you.

Parents
  • It seems fair to assume there is more steel in the conduit than there is in the armour wires of the SWA and the conduit will out perform the armour wires as a circuit protective conductor.

    Maybe calculations may show otherwise?

  • Maybe calculations may show otherwise?

    By and large the SWA strands are adequate, but they cease to be at large CSAs. Yes, conduit almost. certainly has a bigger CSA - there are no gaps.

Reply
  • Maybe calculations may show otherwise?

    By and large the SWA strands are adequate, but they cease to be at large CSAs. Yes, conduit almost. certainly has a bigger CSA - there are no gaps.