What is the purpose of Prospective Earth Fault Current measurement in a 3 phase DB

Good afternoon

On a 3 phase DB what is the purpose of measuring the PEFC?

I know we measure the prospective short circuit current between L1,L2,L3 and N and then double the highest reading. 

This is the Prospective Fault Current which is being recorded.

Why should we waste time with prospective earth fault current?

Are there cases where PEFC is higher than PSSC?

Thanks

Parents
  • Certainly possible - for single phase it's just a matter of a better PE than N (e.g. due to parallel paths on the PE side - e.g. bonding to extraneous-conductive-parts shared with installations closer to the substation for instance).

    3-phase SSC would of course be higher, so there would need to be a more dramatic difference - but still possible in a few cases.

    Of course it might be useful to show that the PEFC is lower (e.g. because RCDs don't have the same breaking capacity).

       - Andy,

  • Andy,

    I struggle to believe that a bolt 3 phase short circuit between all phases could be smaller in magnitude than a fault between any phase and earth

    Thats why I refer to a 3 phase DB and not a 1 phase DB where I know that there are cases where the fault between L and E is higher than the fault between L and N

    Cheers

Reply
  • Andy,

    I struggle to believe that a bolt 3 phase short circuit between all phases could be smaller in magnitude than a fault between any phase and earth

    Thats why I refer to a 3 phase DB and not a 1 phase DB where I know that there are cases where the fault between L and E is higher than the fault between L and N

    Cheers

Children
  • But you're taking L-N and doubling it - so if there's a reduced N in the supply somewhere (reduced N cables were quite common a few decades back - I guess there's still rather a lot still in service) - L might have rather less than half the impedance of your assumptions, so a small PE impedance might still bring the total within the same ballpark.

       - Andy.

  • In some industrial installations the parallel paths from various bits of metalwork: structural steel, pipe work, containment etc provides a much lower impedance path than the actual conductors.