Permanent wiring of an extension lead to a FSU?

I carry out site inspections for a local authority and have recently across a number of 'multiway' extension leads screws to walls and wired directly via a FSU.

The flex cables being either surface run or in plastic box ducting.

Is this compliant with IET regs?

If it isn't, please could someone let me know which specific regulations apply?

Many thanks, Neil

Parents
  • (Not sure if I'm missing some earlier replies)

    Electrically a FCU is pretty much equivalent to a socket and plug, so not much different to a socket supplying a trailing 4-way, or indeed a fused spur feeding a couple of doubles, so I don't see any great objection in principle. Presumably the trailing sockets are of the type with a facility for wall mounting (rather than having been drilled on-site which might undermine some protective measures). If it's supplying lots of small loads, overloading is unlikely to be a problem. If the small loads have high earth leakage (protective conductor current) there might be a concern about c.p.c. integrity, but otherwise for me it falls into the unconventional rather than wrong category.

       - Andy.

Reply
  • (Not sure if I'm missing some earlier replies)

    Electrically a FCU is pretty much equivalent to a socket and plug, so not much different to a socket supplying a trailing 4-way, or indeed a fused spur feeding a couple of doubles, so I don't see any great objection in principle. Presumably the trailing sockets are of the type with a facility for wall mounting (rather than having been drilled on-site which might undermine some protective measures). If it's supplying lots of small loads, overloading is unlikely to be a problem. If the small loads have high earth leakage (protective conductor current) there might be a concern about c.p.c. integrity, but otherwise for me it falls into the unconventional rather than wrong category.

       - Andy.