Neutral Isolation. A Safety Necessity or a Practical Nightmare?
How should regulation 537.2.1.7 be interpreted and applied? This regulation, which I believe has been deleted but is still being followed by some, requires the neutral to be isolated with a linked switch or removable link when carrying out isolation. However, this can cause a lot of trouble and inconvenience, especially for 24/7 departments that need continuous power. The Lead Engineer argues that both supplies, essential and non-essential, need to be isolated to work on the Essential Line side isolator, where the neutral is linked between the line and load. But is this really necessary? Regulation 531.2.2 allows the neutral to remain connected if it can be reliably assumed to be at earth potential. Can this be verified prior to work commencing by a simple calculation of Un-E = neutral current x Zn (TN-S) or a voltage test between neutral and earth? Some suggest that these methods are sufficient and practical, and that isolating the neutral is unnecessary and impractical. Others assert that these methods are not reliable and safe, and that isolating the neutral is essential for safety reasons, even in a well balanced 3 phase system having minimal neutral current and a low Zn. What is your view?
  • if the supply conditions make sure that the neutral conductor is reliably at earth potential.
    Ah, but which "earth potential"? Say you had a TT installation - is your local "Earth" potential the same as Earth at the source? The traditional answer was no - not just because of possibility of the actual soil being at different potentials in different places, but because of certain faults on the network (not just broken PENs but also accidental earthing of line conductors) can mean that the supply's electrode can be dragged very significantly away from 0V. In many ways it seem that what they're trying to say is whether N can be at a significantly different potential to not Earth (as in the potential of the general mass of the earth) but to the installation's earthing system (main earth terminal, c.p.c., bonding conductors etc.). In that context the dependency on being in an installation equipped with main bonding makes a lot more sense.
    I would agree that the new regulation wording doesn't convey intelligible clarity (at least to me).
    There is a bit of an elephant in the room if we carry this thinking to its logical conclusion though - if we take a TN system outside of the main equipotential zone, we might decide that N my at times be at a significantly different potential to its surroundings, and so warrant isolation of N - but then the c.p.c. will be at a similar potential to the N - so shouldn't the c.p.c. be isolated as well?
  • That NZ article is remarkable, and I take away two things,
    firstly that a system of registered electricians is no guarantee of intelligent thought,
    and secondly  that
    While it makes a song and dance about inaccurate test results, clearly no test at all was done really as even a £5 plug in socket checker  would have made it obvious there was a problem.
    Part of me also wonders if there was no RCD in circuit, or if there was but it failed to operate.
    Mercifully both here and there, such events are rare enough to make the news, which I suppose is something.
  • but then the c.p.c. will be at a similar potential to the N - so shouldn't the c.p.c. be isolated as well?
    Enter the argument that leads to the use of double insulated hedge trimmers, lawnmowers etc.
    Arguably if we had not spent most of the 1960s taking them out, you could have provided special 2 pin sockets for double insulated outdoor equipment. Perhaps not the ones with split pins though.,,,
  • • The disconnection of a fixed neutral conductor on TN C S and TN C system is unnecessary and could introduce more significant levels of risk and harm.
    • Disconnection and temporary opening of a Fixed neutral link can result in a situation where the link is not replaced, which can lead to serious con. sequences.
    Always prove dead before commencing working
    Phase to phases
    Phase to neutral
    Neutral to Earth
    • In situations where neutrals are shared the disconnection of the link/conductor can lead to significant voltage instability on dependant connected circuits. in TN-C-S and TN-C.
    Perhaps not always true - say you had local generation as a switched alternative to the grid - the change-over switch would need to switch (and isolate) N to comply with 444.4.7. (Wouldn't be needed in a pure TN-C system of course but the ESQCR prohibits PEN conductors in consumer's installations.)
    That then begs the question, as far as the downstream installation is concerned, how reliable is the N connection with Earth? Moving contacts are generally less reliable than solid joints, and not all disconnection devices guarantee not to close the L contacts if the N has failed to close, or prevent the N from opening if the L contacts have welded closed. If you consider that the N downstream of the change-over switch isn't reliably held at close to Earth potential, can you justify working on such a conductor without isolation?
  • Hi Andy,
    You are right about the generator connection to the system you shall use a 4-pole change-over switch.
    My comment was mostly above the question about the confusion of neutral isolation. With three poles or single pole switch.
    Many thanks
    Arya
  • Note that in countries that use BS7671 but do not have an equivalent to that rule in the ESQCR, your decision may not be the same, and in countries like Ireland , where the underpinning regulations are the same as those that drive '7671, but the national variant is not, then you may well be permitted to permanently connect neutrals to earth consumer side anyway so long as it is safe to do so.
  • Mike.
    If you are in a country using TT or IT systems, then you will install two poles or four poles circuit break or switch to ensure during the isolation, the neutral is disconnected. However, it isn't required in TN-C or TN-C—S system because the neutral is already connected to the earth at the source
    Arya
  • You have explained it very clearly; I want to add when the Electricians carry secure isolation, they have to understand the difference between neutrals in the TN-C and TN-C-S systems. As it connects to Earth at the source and TT system, each property has its own Earth Rod system.
    Guidance Note 3 shows clearly the difference in the diagram
    Arya
  • because the neutral is already connected to the earth at the source
    But isn't N is solidly connected to Earth (i.e. the general mass of the Earth, as defined) at the source for a TT system too?