Alternative solar supply available at point of use Domestic kitchen

Hello newbie : 

Imagine Domestic kitchen Usual array of sockets and under counter appliances

Wish Introduce  Alt solar supply sockets alongside existing grid supply sockets , Thus : User can select alternative ( solar ) supply as opportune arises  at point of use ( battery storage/ inverter system)

Eg plug microwave to alternative socket  as power opportunity ( battery charge is available ) 

(Alt supply sockets are entirely dedicated from inverter as typical OFF grid system ) 

Question  Is there  anything in regs preventing this ; Thought: The sockets must be somehow labelled / identified as alt supply  Any ideas to meet regs? 

Remark : similar to external generator supply but with NO changeover switches . Outlets are dedicated 

thanks Ms Otis 

Parents
  • Regs wise there is nothing stopping a second Ring or Radial circuit being connected to another supply, so long as things are clearly labelled and it is obvious how and where to isolate it if need be.
    However it would be most unusual, and may be a bit confusing for a non- technical user if some sockets were live or dead depending on when the sun last came out. Normally UK practice is that the inverters are "grid tied" that is to say they connect to the house mains, and when generating push current back in the opposite sense to a normal load, so the voltage rises rather than falls  moving from substation to house. That way the socket has a supply all the time, but uses the inverter when available.

    Thinks to watch -

    1) earthing systems will need to be co-ordinated (i.e. solidly connected) so that there is no chance of a user straddling the two systems getting a shock from the cases of one appliance plugged into each.Also, as parts of the system may be live even when the external mains is off, then the external supply  earth cannot be relied upon as the sole means of earthing. -the external earth may be disconnected while it is being repaired.

    2) The performance of the inverter under overload or fault will be very different to the mains supply, and may not be enough to reliably trip a normal breaker. This may mean a non0standard arrangement is needed.

    Can I ask why like this as opposed to the more conventional ?
    Mike.

  • I'd add that many kitchen appliances have starting currents significantly higher than their nominal ratings - it's not just anything with motors or electronic PSU, even simple resistive loads like heating elements will have a much lower resistance when cold. Inverters often struggle to supply such starting currents - and may have to be very significantly over-sized to cope (along with the d.c. side to match). Grid-tied systems avoid such problems as the grid will automatically make up any shortfall.

      - Andy.

Reply
  • I'd add that many kitchen appliances have starting currents significantly higher than their nominal ratings - it's not just anything with motors or electronic PSU, even simple resistive loads like heating elements will have a much lower resistance when cold. Inverters often struggle to supply such starting currents - and may have to be very significantly over-sized to cope (along with the d.c. side to match). Grid-tied systems avoid such problems as the grid will automatically make up any shortfall.

      - Andy.