Alternative solar supply available at point of use Domestic kitchen

Hello newbie : 

Imagine Domestic kitchen Usual array of sockets and under counter appliances

Wish Introduce  Alt solar supply sockets alongside existing grid supply sockets , Thus : User can select alternative ( solar ) supply as opportune arises  at point of use ( battery storage/ inverter system)

Eg plug microwave to alternative socket  as power opportunity ( battery charge is available ) 

(Alt supply sockets are entirely dedicated from inverter as typical OFF grid system ) 

Question  Is there  anything in regs preventing this ; Thought: The sockets must be somehow labelled / identified as alt supply  Any ideas to meet regs? 

Remark : similar to external generator supply but with NO changeover switches . Outlets are dedicated 

thanks Ms Otis 

Parents
  • The house is TN=S

    It might appear to be TN-S, but if you're on the British Mainland, chances are if you were to ask the DNO you'd be told that 'PME conditions apply'. The problem being that for decades now the DNOs have been regularly converting separate N and PE conductors in the street to PEN whenever they do any replacement or repair work (even short lengths mid way along an existing cable) - so your supply carries all the risks associated with PME (TN-C-S) even the combined N/PE conductor doesn't quite reach your cut-out.

       - Andy.

  • hello 

    trying to get back to the question  So should I  tie the off grid  system earth to the main incoming earth  Or bang a copper pipe into the ground ?  

    ciao Ms O 

  • trying to get back to the question  So should I  tie the off grid  system earth to the main incoming earth  Or bang a copper pipe into the ground ? 

    Short answer - both!

    Your "off grid" system will need its means of Earthing, which needs to continue to work if the grid fails, so a local Earth electrode for that. You also have to ensure that everything within reach of each other is on the same earthing arrangement (as any earthing system can, at various times, for various reasons, be substantially different from true earth potential and you don't want people to get shocks between items of equipment just because they happen to be plugged into different sockets (or between an item of equipment and water pipes/taps for that matter). So everything connected together, and to a common bonding system too. That does have consequences - e.g. the off-grid electrode will in effect be an extraneous-conductive-part as far as the grid supply is concerned - so conductors will have to be sized appropriately (maybe 10mm² for a domestic supply where PME conditions apply).

       - Andy.

Reply
  • trying to get back to the question  So should I  tie the off grid  system earth to the main incoming earth  Or bang a copper pipe into the ground ? 

    Short answer - both!

    Your "off grid" system will need its means of Earthing, which needs to continue to work if the grid fails, so a local Earth electrode for that. You also have to ensure that everything within reach of each other is on the same earthing arrangement (as any earthing system can, at various times, for various reasons, be substantially different from true earth potential and you don't want people to get shocks between items of equipment just because they happen to be plugged into different sockets (or between an item of equipment and water pipes/taps for that matter). So everything connected together, and to a common bonding system too. That does have consequences - e.g. the off-grid electrode will in effect be an extraneous-conductive-part as far as the grid supply is concerned - so conductors will have to be sized appropriately (maybe 10mm² for a domestic supply where PME conditions apply).

       - Andy.