Alternative solar supply available at point of use Domestic kitchen

Hello newbie : 

Imagine Domestic kitchen Usual array of sockets and under counter appliances

Wish Introduce  Alt solar supply sockets alongside existing grid supply sockets , Thus : User can select alternative ( solar ) supply as opportune arises  at point of use ( battery storage/ inverter system)

Eg plug microwave to alternative socket  as power opportunity ( battery charge is available ) 

(Alt supply sockets are entirely dedicated from inverter as typical OFF grid system ) 

Question  Is there  anything in regs preventing this ; Thought: The sockets must be somehow labelled / identified as alt supply  Any ideas to meet regs? 

Remark : similar to external generator supply but with NO changeover switches . Outlets are dedicated 

thanks Ms Otis 

  • Ok prelim  reasoning for  modified " standby generator " approach :Ponder if trad inverter grid tie is a bit of a scam? If your not there when the sun shines  Its all to waste ? (Discounting the  now miniscule pay back for regen to grid in off peak times)  .   So makes sense to me: Power when you want it  At point of use .  Yes accept  unaware folks could be confused with unpowered sockets  Adjustment to off grid living ? Outlook global warming> fossil fuels  looks bleak ?  There is always a prominent visual  display of battery status to indicate. .  But yes also devising a timed signal warning for connecting fridge  in case you have forgotten ( LOL) 

    Rather having a parallel off-grid arrangement, have you considered grid tied batteries, with a controller that charges the battery or switches on dispatchable loads (e.g. immersion heater) when there's excess solar and discharges the battery to feed loads there's not. Many inverter manufacturers provide off-the-shelf solutions for domestic applications, with a likely reduction in both equipment and design costs... Most solar installers these days will have a preferred answer that they've used before.

    No need to duplicate circuits or source DC equipment or having to switch sockets over when the batteries are drained, and you retain the benefit of grid support for starting currents etc so somewhat simpler for the user and maintainer. Does mean you can't run in the absence of grid voltage (island mode systems are available but somewhat more pricey), but it doesn't sound like you're too worried about that (and sizing batteries for a reasonable autonomy time will be a big undertaking whichever way you do it).

  • yes solar earth and incoming mains earth should be solidly connected, but in addition you will need an earth electrode(s) of your own, so that all earthing is not lost if for example the external power cable is disconnected during repairs in the street.

    Mike.

  • thank you andy yes accounted for : see my reply to other |: Grid tie uncertain future .Grateful answers to the two unaccounted regs items 

    Labelling and earthing , Ms O  

  • hello  thanks for consideration :  You underline the two potential  show stoppers Labelling / Earthing : Grateful advice 1 and 2 below 

    Ok prelim  reasoning for  modified " standby generator " approach :Ponder if trad inverter grid tie is a bit of a scam? If your not there when the sun shines  Its all to waste ? (Discounting the  now miniscule pay back for regen to grid in off peak times)  .   So makes sense to me: Power when you want it  At point of use .  Yes accept  unaware folks could be confused with unpowered sockets  Adjustment to off grid living ? Outlook global warming> fossil fuels  looks bleak ?  There is always a prominent visual  display of battery status to indicate. .  But yes also devising a timed signal warning for connecting fridge  in case you have forgotten ( LOL) 

    Most grateful for advice 

    1. labelling  identifying  sockets  Propose make them all single  sockets maybe surface mounted Red paint of corner  Notice at visual display of battery status to effect Red sockets have alt supply Isolate at ( invert3er in garage )  Yes am going for the under counter 

    Not very elegant Any suggestions  

    2. Earthing   DC cable solar array will have earth conductor ( mountings) as will inverter power cable supply  The house is TN=S   Should  we should connect the solar installation main earth to the house earth point ? Not separate ? 

    thanks again Ms O 

  • I'd add that many kitchen appliances have starting currents significantly higher than their nominal ratings - it's not just anything with motors or electronic PSU, even simple resistive loads like heating elements will have a much lower resistance when cold. Inverters often struggle to supply such starting currents - and may have to be very significantly over-sized to cope (along with the d.c. side to match). Grid-tied systems avoid such problems as the grid will automatically make up any shortfall.

      - Andy.

  • Regs wise there is nothing stopping a second Ring or Radial circuit being connected to another supply, so long as things are clearly labelled and it is obvious how and where to isolate it if need be.
    However it would be most unusual, and may be a bit confusing for a non- technical user if some sockets were live or dead depending on when the sun last came out. Normally UK practice is that the inverters are "grid tied" that is to say they connect to the house mains, and when generating push current back in the opposite sense to a normal load, so the voltage rises rather than falls  moving from substation to house. That way the socket has a supply all the time, but uses the inverter when available.

    Thinks to watch -

    1) earthing systems will need to be co-ordinated (i.e. solidly connected) so that there is no chance of a user straddling the two systems getting a shock from the cases of one appliance plugged into each.Also, as parts of the system may be live even when the external mains is off, then the external supply  earth cannot be relied upon as the sole means of earthing. -the external earth may be disconnected while it is being repaired.

    2) The performance of the inverter under overload or fault will be very different to the mains supply, and may not be enough to reliably trip a normal breaker. This may mean a non0standard arrangement is needed.

    Can I ask why like this as opposed to the more conventional ?
    Mike.