Alternative solar supply available at point of use Domestic kitchen
Hello newbie :
Imagine Domestic kitchen Usual array of sockets and under counter appliances
Wish Introduce  Alt solar supply sockets alongside existing grid supply sockets , Thus : User can select alternative ( solar ) supply as opportune arises  at point of use ( battery storage/ inverter system)
Eg plug microwave to alternative socket  as power opportunity ( battery charge is available )
(Alt supply sockets are entirely dedicated from inverter as typical OFF grid system )
Question  Is there  anything in regs preventing this ; Thought: The sockets must be somehow labelled / identified as alt supply  Any ideas to meet regs?
Remark : similar to external generator supply but with NO changeover switches . Outlets are dedicated
thanks Ms Otis
  • Question  Is there  anything in regs preventing this ; Thought: The sockets must be somehow labelled / identified as alt supply  Any ideas to meet regs?
    There may be issues with UK legislation (Regulation 21 of ESQCR) if there is no switching to completely disconnect the live conductors of the grid.
    A floating supply or IT earthing arrangement is not recommended in general for domestic use in the UK. Also, Chapter 82 of BS 7671 requires the "backup" supply to be a switched alternative to the grid, not a "floating supply", so really it's not covered in the national wiring code in the UK. One key thing to remember is that, even if the manufacturer only provides one socket-outlet, the first thing users at home will do is connect multi-way extension leads to power equipment, some of which is connected into telecomms installations etc. - so what you thought was "floating" isn't any more.
    See also the following in the IET Code of Practice for Electrical Energy Storage Systems Second Edition:
    • Section 9.4 (and in particular 9.4.5 regarding limitation of use of IT system)
    • Appendix F, item F1 (page 157)
    I'm fairly sure the MCS standard for battery storage installations doesn't permit it either.
    So, in summary whilst product standards, and to an extent installation standards, might appear to permit the use of a "floating backup supply", in practice in the UK for installations that are to be operated by ordinary persons as defined in BS 7671, we would strongly recommend the "floating backup socket" functionality is disabled when the inverter is installed, or, if power backup is required by the client, select an inverter that supports a TN-S earthing arrangement in island mode, along with switching that meets the requirements of BS 7671 and the legislation (Regulation 21 of ESQCR). Relays alone are not suitable for disconnecting from the grid in the UK - the switching device should provide isolation according to IEC 61140.
  • there are some diagrams here https://electrical.theiet.org/wiring-matters/years/2021/84-march-2021/island-mode-earthing-arrangements-new-guidance-in-the-second-edition-of-the-iet-code-of-practice-on-electrical-energy-storage-systems/
    that clarify the proper switching, Graham is one of the authors...
  • If your not there when the sun shines  Its all to waste ?
    Not if you store it in a battery, or an EV's battery (though you may be away in that), or a hot water cylinder.
    The advantage as I see it is that in my home, running the CH boiler for hot water may be unnecessary in the summer. We might even be able to turn off the gas altogether if we get an electric hob.
    The one caveat is that gas energy is 1/3 of the price of electric energy from the grid so the plan only works if at least 2/3 of the energy is "free".
  • hello
    trying to get back to the question  So should I  tie the off grid  system earth to the main incoming earth  Or bang a copper pipe into the ground ?
    ciao Ms O
  • Can I ask why like this as opposed to the more conventional ?
    Because there are a lot of products on the market that do this at the moment, regardless of considerations of UK national requirements?
  • Regs wise there is nothing stopping a second Ring or Radial circuit being connected to another supply, so long as things are clearly labelled and it is obvious how and where to isolate it if need be.
    That's not quite the whole story. See BS 7671, Regulations 823 "An uninterruptible power supply (UPS) is not considered to form part of a PEI ... " because, for "floating socket-outlets", the UPS standard BS EN IEC 62040 is often quoted by manufacturers.
    Also, see BS 7671, Regulations 822.4, 824.2, 826.1.1.1, 826.1.1.2.2, 826.1.1.4,
  • I hope that floating sockets is not what is proposed here - it will need an NE bond either within or without the inverter, and private earth electrodes,  or the normal ADS required for a mix of class 1 and class 2 devices will not be present. That is something to be looked at when the inverter is chosen.
  • trying to get back to the question  So should I  tie the off grid  system earth to the main incoming earth  Or bang a copper pipe into the ground ?
    Short answer - both!
    Your "off grid" system will need its means of Earthing, which needs to continue to work if the grid fails, so a local Earth electrode for that. You also have to ensure that everything within reach of each other is on the same earthing arrangement (as any earthing system can, at various times, for various reasons, be substantially different from true earth potential and you don't want people to get shocks between items of equipment just because they happen to be plugged into different sockets (or between an item of equipment and water pipes/taps for that matter). So everything connected together, and to a common bonding system too. That does have consequences - e.g. the off-grid electrode will in effect be an extraneous-conductive-part as far as the grid supply is concerned - so conductors will have to be sized appropriately (maybe 10mm² for a domestic supply where PME conditions apply).
    Whether this is possible depends on the arrangement in the inverter. Some inverters feed through the Neutral from the AC side, so switching is still required both to disconnect the grid, and connect the earth. Also, you would need to follow the manufacturer's guidance if the inverter backup supply output is designed to be "floating".
    It's not always possible to "reverse engineer" some of the products on the market.
    It's really worth looking at the IET Code of Practice for Electrical Energy Storage Systems as to how the system ought to work.
  • so switching is still required both to disconnect the grid, and connect the earth.
    Although in the OP's suggested case, the inverter output would be permanently separated from the grid supply so no switching involved.  I agree though that some inverters won't have an in-built N-PE link or be suitable for adding one externally - so precluding the possibility of creating an TN-S system for the inverter a.c. side. Separated systems for multiple appliances are prohibited by BS 7671 in normal domestic and similar situations (418/418.3) and an IT system would likely need permanent insulation monitoring (411.6.4), so easy alternatives to TN-S are a bit thin on the ground.