My interpretation of 18th Edition wiring Regs chapter 701 in regards to Zone 0,1,2 in Bathrooms is that electric underfloor heating cannot be used in these zones if 240v as 240v is neither SELV nor PELV i.e. 12VAC, yet I have just asked Warmup and their response was this to my question, are they correct? If so should the 18th Edition not be a little clearer here
Jason 1:18 PM
you are showing electric underfloor heating is bathrooms and even showers, Im confused as I have just read the IET 18th edition and it does not allow 240v underfloor heating in zones 0,1,2 is this correct? if so do you sell 12v underfloor heating?
Welcome Jason! Your request has been directed to the Homeowner department. 1:18 PM Please wait for our operator to answer your call.
Call accepted by operator Lina. Currently in room: Jason, Lina. 1:18 PM
Lina 1:18 PM Hello Jason.
Jason 1:18 PM Hi Lina!
Lina 1:19 PM
It does not allow the controls in the zones, it needs to be outside the bathrooms. But the electric underfloor heating can be in the zones.
Jason 1:21 PM wow, the regs are not clear on this lol
Jason 1:25 PM OK thanks for your help
Lina 1:25 PM You're welcome.
Very much grateful to any responses.
  • The heating elements are presumably not strictly  in the zones, but below the top finish of or within  the floor beneath. Even so I think you need the kind where the element has an earthed jacket/ foil or mesh between the element and anything which if wet could cause an issue.
     Controls and any associated accessible wiring need to be in Zone 2 or ideally  further out.
  • Thanks for your reply Mike, I am grateful for you taking your time to respond. Star
    But of course there is an argument regarding equipment embedded beneath zone 0 but as grout is purous think this would be strongly challenged by building control ;)
    alas I need absolute clarity on the 18th Edition rules, the given the Warmup heating cables are sheathed with earth as specified under Chapter 701.753 however under this chapter it makes no mention of zones... so really it can be argued that as such it can be placed in zone 0 as long as it is IPX7 rated as per 701.512.2 (i):
    701.753 Electric floor heating systems
    For electric floor heating systems, only heating cables according to relevant product standards or thin sheet flexible heating elements according to the relevant equipment standard shall be erected provided that they have either a metal sheath or a metal enclosure or a fine mesh metallic grid. The fine mesh metallic grid, metal sheath or metal enclosure shall be connected to the protective conductor of the supply circuit. Compliance with the latter requirement is not required if the protective measure SELV is provided for the floor heating system.
    But here you can clearly see Warmup think it appropriate to place this 240v cabling in Zone 0, I believe even under the floor you are still in zone 0 alas.
    https://www.warmup.com/warmupedia/questions/can-warmup-electric-heating-installed-shower here makes mention of must be install between 2 non combustible materials though I don't see this in the regs under Bathroom section
    here they show the electric cabling in Zone 0 before tiling  https://support.warmup.co.uk/questions/installation/can-warmup-electric-heating-installed-shower/
  • I'd worry  about  zone 0 - that is normally taken as being inside the bath tub or shower tray Underneath   a one piece tray or tub it is normally taken as outside the zones.
    having said so that is a photo where they are going to tile over it to make the shower floor in sections would worry me a bit.. Does it have an earthed sheath braided over the elements ?.If it does, the way I read it you are OK.
  • Thank Mike
    Here is the context I should have stated with, I intend to instal a wet room where the shower tray is a tiled floor over a wet room former https://www.heatandplumb.com/acatalog/impey-aqua-dec-linear-wet-room-former-ad3l1590 so no actual visible tray, so only thing between the person and the cabling in places is flexible grout between porcelain titles
    The heating wire is earth sheathed braided yes: https://www.warmup.co.uk/underfloor-heating/electric/cables/loose-wire
    And yes makes me nervous putting this un the tiles in the shower, but everywhere I look online specifically those that sell heating cable state you can put in the shower... the idea is great toasty feet when you get in but the possibility of electric shock I take extremely seriously and I work in absolutes so I won't take a Salespersons word for it their product can be used in this way... thought 18th Edition would be a little clearer here, think the 17th Edition was clear as far as I can remember but as much has now been integrated its become murky... I should I suppose air on the side of caution, but Im a kind of person that really wants to know from the horses mouth and if it says Ney then OK ;)
  • Chapter 701.753 however under this chapter it makes no mention of zones...
    Indeed - therefore the usual interpretation would be that the regulation therefore applies without regard to zones - so equally for the whole location.
    The live conductors of the UFH will be fully insulated, covered with an earthed conductive mesh, sheathed and protected by 30mA RCD as well as normal ADS - so the chances of receiving a fatal shock seem pretty miniscule. The earthed braid will act as supplementary bonding for the floor area, so even if the cable were sufficiently damaged to let water get to the conductors, you'd need both a broken c.p.c. and simultaneously a failed and the RCD for the dangerous voltage to persist and even then it would still be almost impossible to generate a potential difference between two different parts of the floor area - you'd need something else earthed and within reach to complete the circuit.
    Compared with say a typical electric shower (bare conductors in an unsealed plastic box, on a 30A+ protective device and for many years not even a requirement for an RCD) the UFH requirements seem rather strict.
  • Ahh a wet room is not really a bathroom - no bath, and the 'zones' are not defined the same way, Even so, if your heaters are inside an earthed braid or similar, and it sound like they are, then even it it ever becomes wet, you are only getting feet to earth potential, so that is deemed OK, after all it is OK to have exposed pipes connected to mains earth.
  • Turn of Phrase, I use Bathroom interchangeable as Shower Room given they both have zone 0.1 in, I was undecided wether to go Wet Room OR Shower Room.
    But you are valid in what you say as there is a clear distinction between Wet Room and Bathroom in terms of Zones but as both share a  zone 0 I felt the distinction was not required in my earlier question, either way Im going into zone 0 "The Danger Zone" just call me Mavric entering into this zone ;)
    Thanks for your input, highly valued, Best, Jason
  • Thanks Andy for your reply, very much valued and read with interest, I agree the chances are so very small of electrocution and it will be installed with upmost attention to detail and any changes in resistance..
    after all I removed an electric shower from the room that was there years with minimal protection and for certain that's not what killed them but old age... I hope lol
  • This is being made far too complicated.
    701.32.2: bottom of zone 0 = bottom of zone 1
    701.32.3: "Zone 1 is limited by: (i) the finished floor level ...
    701.32.4: ditto for zone 2.
    Anything, even a cat's whisker below the surface of the floor is not in the zones.
    Control equipment is a separate matter.
    If you go below the finished floor level, then how would you treat, e.g., the lighting on the floor below?
  • Excellent point and perfect referencing, thanks