Tnc-s on agricultural installations
Hi all.  I am currently doing an Eicr for a large poultry site.  There is 8 broiler sheds.  These are chicken that are specially rared for meat production that we all end up eating.  Now there is a 3 phase 200a supply tnc-s earthing arrangement. The tnc-s earth remains throughout the whole site. Section 705 of bs 7671 and reg 705.415.2.1 at bottom there is note saying that unless a metal grid is laid in the floor, the use of pme earthing facilities as a means of earthing for the electrical installation is not recommended. Looming everyone's thoughts on how you would code this on Eicr. Do u feel it needs changing and converting to tt. Converting to tt brings it own problems with upfront rcd which may give nuisance tripping and power is essential in high density poultry houses to keep ventilation and heating running.  At certain stages of the birds life if power failure for about 30mins can end the lives of thousands of birds .
  • You really need to have a conversation with a network engineer at the DNO to determine the true nature of the DNO earthing system and also determine the generator earthing system, then ensure the earthing system is suitable for use both on and off grid.
    If you want to finalise your EICR you could code the earthing arrangement FI- Further Investigation required.
  • Might it be that the farm is fed from a pole-mounted tx in PNB fashion? In any case, being a rural supply to a relatively large consumer, the LV mains will likely be short and the  risk of loss of neutral or significant N/E voltages will be minimal compared to the apparent mess of the low voltage distribution system in more built-up areas of parts of the U.K. mainland.
    Lots of similar farms here in the north of Ireland. Given the situation you describe, if it the installation was here, personally, I wouldn’t even mention the issue.
    Giving a FI code renders the installation unsatisfactory. That could put the farmer in serious difficulty with the company he supplies to. It may mean that any new crop of birds will be delayed resulting in significant expense to the farmer all because of a note in a guidance document!
    If you are concerned, do the further investigation yourself and carefully analyse your findings to support any decision on giving a code rather than blind, pedantic obedience to 7671.
  • Thank you Lyle for your reply. Yes it is a short cable run from transformer to the metering position. I know the likely hood of loos of neutral is very low.  I have come to the decision not to mention it and leave well alone.  I think I am best taking advice from yourself as I'm I right in saying you  may well have been my tutor this time last year for 2391 inspection and testing course at training Solutions ni?
  • I said could, not would!
    Not my decision to make.
  • Absolutely Sparkingchip, completely agree. Not my decision either. If Adrian was on one of my 2391 courses he will know that I kept my own opinion out of every aspect of the course delivery. However, when dealing with EICRs, I did encourage candidates to carefully consider any codes they might issue and not be a slave to guidance. Whilst guidance is important and reaching out for the opinion of others is often prudent, being confident in one’s deliberations needs detailed understanding of the system under investigation in order to properly evaluate the risks that noncompliance with industry standards might incur.
    That requires inspectors to be significantly above average and whilst acknowledging relevant guidance, they should be confident in the independence of their deliberations. That also means they shouldn’t be unduly swayed by old toss pots like me just because I was privileged to have them in my 2391 class!
  • By the way Adrian, great to have you on the forum. New recruits are always welcome! You will find this forum a very useful sounding board with some of the best in our industry prepared to take time to respond to all sorts of queries in a friendly and measured way.
  • I think the pros outweigh the cons in this situation.If i mention it on my Eicr then the client will feel he needs to act on it, and he is very willing to keep his farm up to date and to a good standard. But say i did take that route and we decided to convert system to TT there is many drawbacks with this .Main one is Rcd protection on the sub mains. 3 sheds are supllied on 1 sub mains, 2 off another and finally one shed on its own along with other out buildings. So a 300ma Rcd feeding 3 seperate sheds .Each of these sheds have got 2 variable speed drives which require type b rcd and will almost certainly from experience give us nuisance tripping of the up front rcd.This along with a lot of other motors and equipment. This i would say is more unsafe for the welfare of the birds than a Tnc-s earthing arrangement. Does anyone think that it would be benificial to add an earth electrode to each submains whilst also keeping the tncs earth. Then in the event of a loss of neutral from the DNO there would still be an earth path?  Or maybe this is a pointless exercise.
  • I spent a long time deciding what to do on a small farm with a single phase supply, having researched the requirements and recommendations as well as trying to get advice from the DNO I converted it to TT, then after a year or so the PV and battery storage installers converted it back to TN-C-S.
  • Does anyone think that it would be benificial to add an earth electrode to each submains whilst also keeping the tncs earth.
    If by an electrode you're thinking of a 4' rod banged into the ground, then I'd vote no. If you had huge steel frame sheds with each upright sunk feet into the ground then perhaps. To be effective you'd want the product of the electrode resistance and neutral current to be < 50 - e.g. something in the order of 0.25Ω for a 200 amp supply - maybe a bit higher if you were confident the loads would always be reasonably balanced across phases, but you're probably still looking at 'reasonably difficult' territory, Also consider the potential rise of the ground around the electrode(s).