AFDD on minor works ?

I've a really small job to quote  ( adding a fused spur off an existing radial )  in a care home ,with a decent , but fairly old wylex board  . am  i right in assuming i have to fit an AFDD ?? , I know i would if it was a new circuit being installed , but being only a fused spur off an existing radial , it seems a massive expense for what is supposed to be an easy job ??  can't seem to find any conclusive answers on line anywhere .

any thoughts would be appreciated 

Parents
  • The requirement only applies to circuits supplying socket outlets (421.1.7) so as long as your addition doesn't include a socket, I don't see a requirement to add an AFDD. There's no blanket requirement to bring existing up to date even if it's on the same circuit as the new work - only the new work itself needs to comply.

    Doesn't help if you were adding a socket of course.

      - Andy.

Reply
  • The requirement only applies to circuits supplying socket outlets (421.1.7) so as long as your addition doesn't include a socket, I don't see a requirement to add an AFDD. There's no blanket requirement to bring existing up to date even if it's on the same circuit as the new work - only the new work itself needs to comply.

    Doesn't help if you were adding a socket of course.

      - Andy.