Loop Impedance Tests

I did a loop impedance test today at a garage socket with ATT on and got a measurement of about 250Ω, I did it again without ATT and measured about 2.5Ω. I have noticed small discrepancies before, but never on this scale. I did repeat the tests, and am fairly sure I was reading the display properly! The house is PME, presumable exported to the garage. I didn’t have time to investigate further, and am going back on Monday so can look into it further then. I am wondering what could cause such discrepancies. My meter has fairly new batteries in it.

Parents
  • Did you take a reading at the CU ?  Might be caused by dirty socket contacts. Try a dead test at the terminals of the socket.  Might be time for a new socket face. Garages are dirty places.

    Gary

Reply
  • Did you take a reading at the CU ?  Might be caused by dirty socket contacts. Try a dead test at the terminals of the socket.  Might be time for a new socket face. Garages are dirty places.

    Gary