Long meter tail upgrade, no nice solution comes to mind.

Hi All.

Thought I'd open this one up for discussion as I'm sure some of you can come up with a nice solution.

I've been given a friendly notice that i need to do something about the meter tails in my house by my DNO following the installation of a smart meter. They're the wrong gauge for the master fuse (16mm2 on a 100A fuse) and too long, about 4m. I'm having a job coming up with a solution I like. The current installation is original from when my house was built in 1996 and has gone unnoticed until now.

The meter is in a box on the front wall of the house and the tails exit this, run up the inside of the wall and over the ceiling of what was originally a bin cupboard in an uninsulated roof space before entering the distribution board directly though the hallway wall. The logical thing to do would be to protect the tails by replacing them with SWA but I have two problems with that. 1 that I have no way of terminating the SWA in the meter box without invading the DNO's space and 2 I'm not confident in brining in SWA from behind the board, as I'd effectively have to terminate it long and push some excess back into the roof space, and end up with the SWA termination in the wall screwed to the back of the board. So I can see this option needing me to bring the SWA in from above or below the board which would be ugly as sin in my hallway, doubly so as it'll have a bend radius easily measured in miles.

So I've considered using Steel Conduit instead, as that should be as tough as SWA. However unless I've missed something the largest I can get is 32mm OD which has an ID of circa 27mm. As I'm expecting some quite high temperatures in the roof space during the summer 25mm2 (rated to 101A if I'm reading Appendix 4 properly) could well end up under rated in the summer, so I'd be best to use 35mm2. This has a max OD of 13.5mm according to Doncaster cables meaning it'll be tight getting 2 down it.

I considered using XLPE Insulated 25mm as that can run hotter but of cause there's the 70 degC conductor limit of the board so it's not a help.

Bringing my back to SWA again.

I don't want to put joints in above the bin cupboard as there's no way of inspecting them.

So any other ideas of what I could do to protect the cables sufficiently to ignore the limits?

Thanks in advance.

Parents
  • If you can get into the bin cupboard from the meter box run standard 25mm tails (and a 16mm earth as the existing on is probably 10mm) into the bin cupboard and fit a switch fuse in there. Then carry on in standard 25mm tails through the wall to the CU.  Presuming i am reading your description properly.  Use a bit of galv or plastic 2x2 or 3x3 trunking to tidy the cables up.  No rcd required on the tails. 

    35mm tails is  OTT

    Gary

Reply
  • If you can get into the bin cupboard from the meter box run standard 25mm tails (and a 16mm earth as the existing on is probably 10mm) into the bin cupboard and fit a switch fuse in there. Then carry on in standard 25mm tails through the wall to the CU.  Presuming i am reading your description properly.  Use a bit of galv or plastic 2x2 or 3x3 trunking to tidy the cables up.  No rcd required on the tails. 

    35mm tails is  OTT

    Gary