Back to 'basics' - in reality but with respect to Regs definition, what is the [main] earthing conductor and its CSA

Good morrow

"Earthing conductor. A protective conductor connecting the main earthing terminal of an installation to an earth
electrode or to other means of earthing" :

Is it the DNO strapped conductor (could be a few steel strands) around the sheath of the supply cable into the MET, or the DNO conductor out the side of the Service Head into the MET  ?

Is it the conductor that runs out the side of the Service Head (or from the supply cable sheath) up into a consumer unit 'MET'  ?

Is it not, however, the conductor(s) running from the MET up to the [sometimes multiple] db/cu earth bar(s)  ?

As an aside,  how does one determine the CSA of the DNO provided earthing conductor (as defined)  to put on the EIC/EICR   ?

Regards, Habs

Parents
  • Is it the DNO strapped conductor (could be a few steel strands) around the sheath of the supply cable into the MET, or the DNO conductor out the side of the Service Head into the MET  ?

    Either. The former sounds like TN-S with a PILC cable - those strands will be copper (mine at home are 4 x 4 mm²); the latter would be a TN-C-S supply.

    Is it not, however, the conductor(s) running from the MET up to the [sometimes multiple] db/cu earth bar(s)  ?

    If there is nothing else in the terminal bar (main bonding) I think that you could regard the two pieces as one. Otherwise that bit is the CPC of the meter and consumer tails.

    As an aside,  how does one determine the CSA of the DNO provided earthing conductor (as defined)  to put on the EIC/EICR   ?

    With a micrometer or a good quality pair of (electronic) callipers.

Reply
  • Is it the DNO strapped conductor (could be a few steel strands) around the sheath of the supply cable into the MET, or the DNO conductor out the side of the Service Head into the MET  ?

    Either. The former sounds like TN-S with a PILC cable - those strands will be copper (mine at home are 4 x 4 mm²); the latter would be a TN-C-S supply.

    Is it not, however, the conductor(s) running from the MET up to the [sometimes multiple] db/cu earth bar(s)  ?

    If there is nothing else in the terminal bar (main bonding) I think that you could regard the two pieces as one. Otherwise that bit is the CPC of the meter and consumer tails.

    As an aside,  how does one determine the CSA of the DNO provided earthing conductor (as defined)  to put on the EIC/EICR   ?

    With a micrometer or a good quality pair of (electronic) callipers.