BS 7671 permits RLV to be used anywhere, but it's only mandated on construction sites.
According to BS EN IEC 60209-2, there is really nothing to prevent the 4h-keyed yellow plugs and socket-outlets from being used on either system.
This would really be an observation to discuss with the duty-holder, as it's their H&S / electrical safety risk assessment at the end of the day. I agree that the system does not offer any additional safety over a 230 V supply at present, and so it's a fair question to ask. However, unless 10 or 30 mA RCD protection has been omitted (which you don't discuss yourself, but has been mentioned by others) it does not appear, at least from the information provided in this thread, to be a non-conformity with BS 7671.
However, if 30 mA or 10 mA RCD protection is not provided for socket-outlets with rating not exceeding 32 A, I would definitely consider providing a coding.
BS 7671 permits RLV to be used anywhere, but it's only mandated on construction sites.
According to BS EN IEC 60209-2, there is really nothing to prevent the 4h-keyed yellow plugs and socket-outlets from being used on either system.
This would really be an observation to discuss with the duty-holder, as it's their H&S / electrical safety risk assessment at the end of the day. I agree that the system does not offer any additional safety over a 230 V supply at present, and so it's a fair question to ask. However, unless 10 or 30 mA RCD protection has been omitted (which you don't discuss yourself, but has been mentioned by others) it does not appear, at least from the information provided in this thread, to be a non-conformity with BS 7671.
However, if 30 mA or 10 mA RCD protection is not provided for socket-outlets with rating not exceeding 32 A, I would definitely consider providing a coding.