110v industrial sockets

I have come across some 110v industrial sockets (BSEN60309) which are installed in a utilities company's premises and which are not installed as Reduced Low Voltage (RLV) as detailed in BS7671.
I do understand that the RLV is required for constructions sites and similar premises due to the method of connection of the secondary which had a Line to Earth voltage of 55V.
The ones I have encountered have the Earth pin of the yellow 110v sockets connected to the primary earth, and when tested at the sockets there is 110v Line to Earth, and there is no connection of the Earth pin to a centre tapping of the double wound 240/110v transformer.
My thoughts are that, although the premises is not actually a BS7671 section 704 location, it does actually present similar hazards that might be encountered on a building site, and that having decided to install 110v sockets, presumably for safety reasons, why would you not ensure they were RLV where I believe there are no known incidents of electrocution?
I cannot find any guidance in the Safety First Best Practice Guide as to if a Classification code should be applied, but I am thinking that as an absolute minimum, the client should be informed in writing of the situation.
What do others think?
Parents
  • I agree that this sounds very odd and consider that it MIGHT be a mistake.

    Definitely ... I know a lot of large companies have "electrical procedures" that mandate that all non-battery electrically-powered single-phase power tools are supplied by a safety transformer with a 55-0-55 V centre-tap-earthed secondary.

    In which case, this does not conform to the company's safety procedures (and could mean the company is exposed to the possibility of a HSE prosecution if there is an incident).

    It's therefore absolutely imperative that it's discussed with the duty-holder!

Reply
  • I agree that this sounds very odd and consider that it MIGHT be a mistake.

    Definitely ... I know a lot of large companies have "electrical procedures" that mandate that all non-battery electrically-powered single-phase power tools are supplied by a safety transformer with a 55-0-55 V centre-tap-earthed secondary.

    In which case, this does not conform to the company's safety procedures (and could mean the company is exposed to the possibility of a HSE prosecution if there is an incident).

    It's therefore absolutely imperative that it's discussed with the duty-holder!

Children
No Data