Dual RCD boards are unlikely to be suitable for EV charging installations even with type A or B RCDs, discuss

I’ll paraphrase Regulation 722.531.3.101, “each charging point shall be protected individually by an RCD”. With that in mind a dual RCD board where both RCDs protect multiple circuits will not be suitable as the requirement is for the charge point to be individually protected. The reason I open this up to discussion is because so many installers seem completely unaware of the wording of 722.531.3.101 as about 50% of the installations I see the charger is protected by an RCD protecting multiple circuits, in particular new builds were the provision for electric vehicle charging has been made during development. I also often give quotations to prospective clients where they’ve already had at least one quotation where the previous installer has said “great you’ve got a spare way in your dual RCD board, so we can use that” and I’m thinking “erm no you can’t”

Parents
  • what tends to happen is they install an SWA cable on a 32A MCB which is terminated on the driveway in a wiska box… technically it’s fully compliant as it would only be non compliant when the charger itself is installed…

    Am I missing something here? Provided the EVSE has 30mA RCD protection included - which most seem to claim they do (presuming it does actually comply with the required standards, which has been questioned for one or two models) wouldn't 722.531.3.101 be satisfied even if the circuit was fed by an MCB?

       - Andy.

  • Using a Granny Lead (Poor choice of name in my opinion) would take days to charge an EV but it is an accepted method when there is no other option as a get you out of a predicament  Its not a long term solution.

    The other thing to consider is the average home buyer does not know what an EVSE is and they do not know what to look for.  So when the marketing brochure state EV ready they Assume rightly or wrongly it means ready to just park your vehicle and start to charge it. 

  • The other thing to consider is the average home buyer does not know what an EVSE is and they do not know what to look for.  So when the marketing brochure state EV ready they Assume rightly or wrongly it means ready to just park your vehicle and start to charge it. 

    Are people really so gullible?

    Perhaps they are 'cos the show houses are bound to have been fitted with an EVSE.

    Back to the CU ...

    Does it really matter because if the installation has been done properly and appliances are fit for purpose and well-maintained, nothing should ever trip.

  • The average person does not know or understand Electrics.  They pay an electrician who they Assume (rightly or Wrongly) does the job correctly and to the current standards/regs of BS7671.

    Now the issue is that sometimes the Sparky or the Designer do not know what is what or there is confusion or mis-leading/mis-guiding information.  Controversial statement I know.  Eg. Take a domestic dwelling RCBO.  
    MCB Trip curve B eg a B6 and RCD Class A or Type A
    Now look at the front of an RCBO and it states B6 so some people think or may think they have a RCBO type B.  Bargain at only £15 to £20.  The informed people will say the B6 is the MCB side and the icons will tell you the RCBO side.  Then there is the other elephant in the room.

    Single Pole

    Double Pole

    Single Pole with switched neutral or solid Neutral

    Again this could confuse us on the best of days. 
     

  • Now the issue is that sometimes the Sparky or the Designer do not know what is what or there is confusion or mis-leading/mis-guiding information.  Controversial statement I know.  Eg. Take a domestic dwelling RCBO.  
    MCB Trip curve B eg a B6 and RCD Class A or Type A
    Now look at the front of an RCBO and it states B6 so some people think or may think they have a RCBO type B.  Bargain at only £15 to £20.  The informed people will say the B6 is the MCB side and the icons will tell you the RCBO side.  Then there is the other elephant in the room.

    This example of "confusion" cannot be addressed in BS 7671 ... marking and classification of circuit-breakers, RCCBs and RCBOs is mandated by the relevant product standards.

    You will notice that there is no real confusion, though, in terms of marking on the product ... B on an RCBO does not relate to classification of residual current operating characteristics, which are identified by one or more relevant symbols, as illustrated in Guidance Note 3 here:

    So, is the confusion actually coming about in the technical specifications and descriptions?

  • Is the above explanation made clear in the latest OSG (On Site Guide) I do not have one to hand?

    People find the explanations in the OSG easier to understand than BS7671 and often the OSG is their Go To reference guide while on site

  • I don't think so, that Figure is from Guidance Note 3: Inspection & Testing, 9th Edition.

  • May I suggest it gets added to OSG for the next revision?

  • This is just a matter of keeping oneself well informed of what is required in terms of personal CPD… up to a point competency schemes should be on top of it as well. 
    There’s no excuse for a jobbing sparks to not know what a B type RCBO with A type RCD characteristics is, and the difference between double pole, single pole (solid neutral) and switched neutral are and how to identify the symbols on the devices… after that it’s about being aware of which ones you as an installer need for the kind of installs you do.

  • I do understand that people should keep up with CPD..  It is not always the jobbing Spark doing it.  Some times the Designer is getting it wrong and the installer just go ahead with what is on the plan or diagram.  Sometimes the installer is not fully qualified or competent and they may be 1 of 10 with only one QS on site. 

    This also brings up an interesting discussion.  Lets say the Designer or installed read the MI (manufacturers Instruction) for MyEnergy Zappi 2 to 3 years ago or they went on the installer course.  Now we know the Zappi does not comply to BS7671 with regards to the RCD protection so MyEnergy are now telling customers the Installer done it wrong.  However the Installer followed the MI issued at that time for the install done at that time. 

  • May I suggest it gets added to OSG for the next revision?

    I will forward to the relevant department at the IET.