I have a situation on a caravan site were the sub distribution boards are fed from the main DB via a SHNEIDER nsx MCCB which as a Zs of 0.45 ohms. Zs earth is taken car eof via 300mA rcds, but tlive to neutral Zs on the sub board is is 1.84 ohms(TNC-S). That gives me a problem with the MCCB not tripping in the event of a short circuit. Any suggestions?

Parents
  • A possible solution to your problem is to verify the actual disconnection time for your short circuit at that level of impedance and ensure that it complies with regulation 434.5.2.

Reply
  • A possible solution to your problem is to verify the actual disconnection time for your short circuit at that level of impedance and ensure that it complies with regulation 434.5.2.