BS7671 - It's A School Day (Every day is a school day)

Something to ponder for a Friday


Should the period of inspect for schools fixed electrical systems be shortened from 5 years to 3 or even made annual?

Should schools for under 16 years be granted special location status in BS7671?

Should all circuits in schools be protected by a 30mA RCBO/RCD regardless of their use?  This would apply to new or existing circuits.

Should schools have an accessible earth rod/disc and an inspection pit?


As always please be polite and respectful in this purely academic debate. 



Come on everybody lets help inspire the future.

Parents
  • Should all circuits in schools be protected by a 30mA RCBO/RCD regardless of their use?  This would apply to new or existing circuits.

    Absolutely not - schools are often large and complex electrical installations with many sub-mains/distribution circuits - putting 30mA RCD "protection"  on them would result in many unneeded disconnections and so create extra hazards resulting from the loss of power (everything from lighting to kitchen refrigeration), not to mention loss of teaching time.

       - Andy.

  • Hi Andy

    My intention there was for Final circuits rather than distribution circuits but I do see your point about unneeded/unwanted disconnections.  I do wonder how this will change when schools start to have EVSE and Solar PV fitted?

Reply Children
  • I do wonder how this will change when schools start to have EVSE and Solar PV fitted?

    It's already happening - the primary school near me had most of its south facing roofs covered in panels over last summer, and I doubt it was the first. What difference would it make though? - as they won't be downstream of other final circuits.

      - Andy.