Reverse Polarity
Has anyone encountered a reverse polarity single phase PME supply to a house? If so, how did it happen and how was it detected?
I am intrigued to how you would discover it by measuring L-N, L-E, and N-E at the incoming side of the Main Switch, as the Earthing conductor would be connected to the Line at the cut-out and give 0V, the same as if it were correctly wired and you were measuring N-E?
I cannot get my head around how you would detect the issue.... maybe I will set it up on an empty standalone C/U and see what I get?
  • What about making voltage measurements referenced to a independent earth electrode?
  • I am intrigued to how you would discover it by measuring L-N, L-E, and N-E at the incoming side of the Main Switch, as the Earthing conductor would be connected to the Line at the cut-out and give 0V, the same as if it were correctly wired and you were measuring N-E?
    Indeed it would. It becomes more obvious at the "edges" of the equipotential zone where there's some true earth reference about. Holding class 1 equipment while standing on damp solid floors indoors or outside touching a bonded tap.
    I haven't come across the situation personally, but I do vaguely recall a report of a case ... detected via an unwisely bonded metal garage door if I recall correctly - with an unfortunate result.
    If in doubt, test to an independent earth reference - e.g. screwdriver in a flower bed - is often the best course.
  • Might might be able to achieve the same effect using a non-contact voltage indicator, or if you like living dangerously . . . a neon screwdriver!
    All joking aside, please don't use a 'neon screwdriver' . . . mentioned to illustrate the concept only! Slight smile
  • So L and N are reversed.
    Normally, L-N and L-E = 230 V, N-E = 0 V.
    When reversed, L-N = 230 V, L-E = 0 V, N-E = 230 V.
    If I am missing something, I apologise.
  • it depends which 'E' you mean Chris, the CPC one that is derived from the PME neutral and appearing on the top of the 3 pin sockets, will be at neutral potential and no fault will be detected on the meter.
    However, the one that comes in via the plumbing will be a 'terra-firma' earth and will indeed correctly indicate the reversal.
    As others have said, it is where the CPC/ equi-potential zone meets the true earth - outside taps, EV chargers, outside lights and lamp posts etc are where the error will first be spotted.
    Also we tend to assume that the DNO earth electrodes always give a  better (lower resistance) earth connection than the bonding  at the load (property).
    That is not always the case, especially with modern plastic clad cables or overhead supplies, especially with some steel pile building constructions.
    In that case when the 230V is split between the DNO electrode and a large local electrode - either by design or accidentally by structural bonding,  it may be that the local earth looks OK, and everyone else on the substation gets shocks from the CPC , The larger fault current means the neutral (star) point of the transformer is pulled a long way off true earth. (In extremis you could imagine the corner of the 3 phase delta being earthed at the load, instead of the centre star, so that you have one phase near earth, the  neutral of 230, and the other 2 phases at  about 400V)
    Lots of current then flows in the earth between the house and the transformer but as none of it is via a meter, it may take some time to get tracked down,
    Rare but not unknown.
  • The neutral and 'earth' of a PME supply are common in the DNO service head, so if polarity is reversed at or before that point, the neutral and 'earth' will be at the same potential and the voltage measurements between phase, neutral and earth will all appear correct :
    L-N = 230 V   L-E = 230 V   N-E = 0V
    However, if the voltage measurements are made with reference to an independent earth electrode 'X' :
    L-N = 230 V   L-X = 0 V   N-X = 230 V   and also   E-X = 230 V
    Does that help at all?
  • Does that help at all?
    Not always ... because if the MET is connected to extraneous-conductive-parts, all sorts of strange things start to happen. Sometimes, things will appear "normal", at others it can appear that exposed-conductive-parts have a (sizeable) voltage with respect to extraneous-conductive parts (or the "floor").
  • Yes - the effect of other 'earthy' connections to to the MET is something I didn't take into account in the simplified model above.
    I thought that GN3 contained a note about verification of the polarity of the incoming supply - however, if it ever did it must have only been in older editions as it doesn't seem to appear in the current edition?
  • Thankyou for all the comments. My main concern would be with a Line to Neutral reversal of a PME supply somewhere external to the property (e.g. DNO network), which would not be obvious or detectable by visual inspection during initial verification of a new electrical installation. I am struggling to see how the standard method that an electrician would undertake when checking for correct 'Live' Polarity at the origin (testing L-N and L-E = 230 V, N-E = 0 V) would highlight the problem?
    Possibly better to describe as L-PEN (or L-CNE) reversal.