Reverse Polarity
Has anyone encountered a reverse polarity single phase PME supply to a house? If so, how did it happen and how was it detected?
I am intrigued to how you would discover it by measuring L-N, L-E, and N-E at the incoming side of the Main Switch, as the Earthing conductor would be connected to the Line at the cut-out and give 0V, the same as if it were correctly wired and you were measuring N-E?
I cannot get my head around how you would detect the issue.... maybe I will set it up on an empty standalone C/U and see what I get?
  • I would like to think that the DNOs have a means of confirming correct polarity, but I have struggled to find anything online.
    I would have thought in most cases simple inspection would be enough - when  Ls are cores and Ns are concentric - it's pretty obvious there's something wrong if someone tries to connect core to armour or vice versa. Easier to make a mistake with open wire overheads (but they don't usually serve PME installations) which really only leaves ABCs - I'm not sure if they have a foolproof way of distinguishing PENs from live conductors then (other than the number of 'ribs' in the insulation).
  • It could get reversed in several ways, common occurance is when the meter is changed
    At the main cut out
    At the meter
    At the CU/DB
    At the socket
    Ways to check
    At the main cut out L should be on the fuse carrier side can confirm with a Contact stick and/or GS38 to E and/or lamp meter L to E.  N will not light lamp or sound contact stick
    At the meter N should be the 2 middle cables can confirm with a Contact stick and/or GS38 to E and/or lamp meter L to E.  N will not light lamp or sound contact stick
    At the CU/DB Contact stick and/or GS38 to E and/or lamp meter L to E.  N will not light lamp or sound contact stick
    At the socket use a 3 pole plug in tester or use MFT to test polarity
    If there are connector blocks in the mix they are also a source where polarity can be reversed.
  • At the main cut out L should be on the fuse carrier side can confirm with a Contact stick and/or GS38 to E and/or lamp meter L to E.  N will not light lamp or sound contact stick
    LAmp/ meter will not work on a PME supply if the 'E' you use is (due to reversal) the live one.  In a well isolated location - like an upstairs maisonette fed by plastic water pipes or something, you could have the whole installation CPC alive and not feel very much, and the tester may show good when it isn't
    The non contact probe may or may not work as well as you expect, depending on how much of an equipotential zone the building made - don't forget that the second terminal of the volt-stick is the capacitance to the local environment, augmented by that of the user.
    I have heard of both L and N/E showing as live for a non-contact tester, but not seen it myself.