Should the humble domestic MET (Main Earth Terminal) be retired

Should the humble domestic MET (Main Earth Terminal) be retired and be replaced by Green coloured Henley style connector block?

Things to consider

More electronics in the dwelling naturally leaking mA to Earth in normal operation

Connector block is safer as has no exposed terminals thus introducing an IP rating

With more and more PEN faults occuring on the network.  A domestic install could have the Earth/Earth Bond become a live conductor under fault conditions.  Under certain PEN fault conditions the MET could be at 230v nominal.  This also opens up the debate of

if a 16mm CSA Earth cable is wise if the tails are 25mm CSA.  (again 16mm CSA under PEN fault conditions)

As always please be polite and respectful in this purely academic debate.


Come on everybody lets help inspire the future.

Parents
  • I won't repeat comments about exposed-conductive-parts and extraneous-conductive-parts being at substantially the same potential as the MET.


    However, a plastic cover might help keep dirt and dust out ... and possibly make it less prone to "tampering" ... those would be benefits for me.

    Green coloured Henley style connector block?

    If it were green-and-yellow, OK, but not the single colour green, that would have to be otherwise marked I'm afraid.

    It also won't take away the need for a warning notice to meet the requirements of 514.13.1.

Reply
  • I won't repeat comments about exposed-conductive-parts and extraneous-conductive-parts being at substantially the same potential as the MET.


    However, a plastic cover might help keep dirt and dust out ... and possibly make it less prone to "tampering" ... those would be benefits for me.

    Green coloured Henley style connector block?

    If it were green-and-yellow, OK, but not the single colour green, that would have to be otherwise marked I'm afraid.

    It also won't take away the need for a warning notice to meet the requirements of 514.13.1.