Bonding of a bolted-together equipment rack located in a vehicle

I have a custom built stainless steel equipment rack that is made up of many individual sections of stainless steel angle that are bolted together to form the complete rack. The stainless steel parts will not have any paint or finish applied. 

The equipment rack will be mounted in a vehicle with the bottom sections of the rack bolted to the metal floor of the vehicle. 

The equipment rack will have 12 Volt and 28 Volt equipment mounted on it.

My question.....

- Does a single wire connection from the vehicle's Main Earth Terminal (MET) to the equipment rack meet the protective bonding requirements?

I am hoping that I do not need to have a separate wire from the MET to each individual piece of steel angle, or a 'strap' linking the bolted-joints.


Parents Reply Children
  • quite. Assuming decent construction - that is using shake proof washers or similar- I'd be happy to omit bonding between anything that passes a 'beep' test with a meter on the continuity range reading  - to within a last digit flicker reading the same as the test leads. If need be document the results.

    Bonding is more important between parts that can become separated in normal use, like doors on lift off hinges, and even then personally I prefer finger stock or spring contacts, as bond wires tend to get broken off and not noticed

    And of course it matters more in structural parts that carry current by design, such as in when the vehicle chassis carries return current from a light fitting via its bracket or something, which is not really what you seem to be doing.

    regards Mike.

  • Thanks for the input, much appreciated.

    Given the comments, I will fit a single wire to the overall rack and shall ensure all bolted joints have shakeproof washers, and will probably use nylock nuts too.

    In the worst case scenario, I can always retrofit additional bonds.

    I have access to a milliohm meter, so can easily check that all parts are equipotential (within a given number of millohms).

    Tha is again for the input. 

  • If you are not sure how many milliohms to worry about, and actually want a figure, you can estimate if you can  decide what the worst credible fault is - perhaps a short from a battery supply fused at 10A would need to drop no more than a few % of the battery voltage at 10A, to ensure a fast and reliable 'pop' with a few times 10A, without overheating the bonded part too much in that time. 

    So for an item that could credibly short to a cable fused at 100A, the bonding requirement needs to be that much better than if the requirement was to operate a 10A fuse. If you can be sure that the fault condition is incredible - if the insulation chafed off and then the wire snapped it still would not reach, sort of thinking, then you do not need to worry about that current path at all.

    In vehicle battery systems where the voltages are lower and the currents higher than mains practice, the impedance can easily be beyond the lower limits of a normal meter, and then not worth trying to measure,  rather things are just bolted up nice and tight onto clean metal and the resistance calculated/estimted. Usually fixing metal work gives you lots of cross-sectional area, and even in a large vehicle the distances are quite short.

    (For an extreme example a motorized tank turret I think was 200-300A at 24-28V - so to blow the 500A fuse fast needed a reasonable multiple of that, say about 2000- 3000A , so that needed (and had) a return path of less than ten  milliohms or so. (1mm2 copper is 16-19 milliohms per metre, but you should also consider the adiabatic heating of that.) The tank cables were something like 35 or 50mm2 - I am quite sure your case is much less extreme !! These figures are not exactly right, being dragged from memories of a conversation many years ago with someone who worked on the controllers for the things.)

    Note that your earth wire may need to be reasonably chunky for mechanical strength, even if low current handling, unless protected. The normal 7671 rules used at 230V are not really what you need but there is some read-accross of the ideas.

    Mike.

  • Hi Mike,

    Thanks for the extensive reply.

    To be honest, I'd not actually considered the DC current fault scenario at all, so I will be taking a look at that over the next day or so. The DC fault current could be in excess of 100 Amps. 

    My primary concern was and still is compliance to the regulatory requirements for "protective equipotential bonding" that apply to metalwork that's fitted into a vehicle, when there is 240 Vac present in the vehicle. Note - I have just noticed that I didn't mentioned there was 240 Vac in the vehicle. However, there is no 240 Vac equipment or cabling in/on the equipment rack.

    My original concern about a possible need to bond every separate piece of metal that makes up the equipment rack came from a statement that  I read in the following article: https://electrical.theiet.org/media/1187/electrical-installations-in-caravan-camping-parks-caravans-and-motor-caravans.pdf. Specifically the statement "Regulation 721.411.3.1.2 requires structural metallic parts that are accessible from within the caravan to be connected through main protective bonding conductors to the main earthing terminal within the caravan."

    Steve