Bonding of a bolted-together equipment rack located in a vehicle

I have a custom built stainless steel equipment rack that is made up of many individual sections of stainless steel angle that are bolted together to form the complete rack. The stainless steel parts will not have any paint or finish applied. 

The equipment rack will be mounted in a vehicle with the bottom sections of the rack bolted to the metal floor of the vehicle. 

The equipment rack will have 12 Volt and 28 Volt equipment mounted on it.

My question.....

- Does a single wire connection from the vehicle's Main Earth Terminal (MET) to the equipment rack meet the protective bonding requirements?

I am hoping that I do not need to have a separate wire from the MET to each individual piece of steel angle, or a 'strap' linking the bolted-joints.


Parents
  •   

    It depends if a ground wire is run to the equipment of if it is grounded through the steel rack.

    If you put steel storage racking in the back of your van you would not bond it, if you were to screw a DC 12 V Makita cordless  battery charger into the rack you would only have to run one conductor to it from the vehicle fuse board or wherever you get the supply from, the other conductor can simply be grounded to the rack or the vehicle body, so long as there’s continuity, I cannot imagine many people are going to “bond” the rack as such.

    If the vehicle was live at 230 volts you are inside a Faraday cage formed by the bodywork, you would be fine until you tried to get out and put a foot onto the ground outside of the vehicle.

    If the rack is inside the Faraday Cage and not extraneous, is there going to be an issue?

    If you are in a vehicle that is caught up in electric cables, DO NOT TRY TO GET OUT!

    www.fwi.co.uk/.../cool-headed-tractor-driver-unharmed-power-cable-smash

  • Nevertheless a conductor required for grounding is not bonding.

Reply Children