722.411.4.1 installing sp evcp with LOP on a 3ph&n supply tncs

Installing single phase ev charger on a sp db fed from a 3phase&n supply origin 722.411.4.1 indent (i) was deleted after blue regs book to brown book, , also indent (iv)&(v) added  along with (iii) in brown current regs book, amd2  so am I correct in thinking this is OK to install now with built in lop o-pen on a tncs tp&n supply,

Parents
  • Indent (i) was about 3-phase installations that had extremely well balanced loads, so that even if the supply PEN conductor became severed, the consumer's end of it would remain at a safe voltage (pretty impossible to guarantee in practice),  so that one's deletion probably isn't relevant.

    The other change, the removal of the single phase condition from intent (iv) however, does open the door to using L-N voltage sensing open-PEN devices on installations with 3-phase supplies.

    Just be aware that there are disadvantages to the L-N voltage sensing approach to open-PEN detection - specifically that where a 3-phase distribution system is involved it is possible, under certain conditions, for c.p.c to be at a hazardous voltage but the L-N voltage still to be within normal range. So as a designer you might like to consider whether alternatives might be better choices. 3-phase open-PEN detectors that compare the PE or N voltage with an artificial N point created from the 3 lines, don't suffer that particular blindness for instance. Or where tbe EV and EVSE would be well away from anything on the PME system, TT might be an option.

       - Andy.

  • it is possible, under certain conditions, for c.p.c to be at a hazardous voltage but the L-N voltage still to be within normal range.

    Whilst what Andy said here is true, it's not a statement  that can easily be demonstrated to be low or high probability of serious electric shock in given circumstances, and is certainly not the whole picture.

    This seemingly simple statement ignores the fact that rarely in three-phase systems is the phase balance maintained for long periods. In a real broken neutral situation, the line to neutral voltages on all phases constantly change. So if the broken PEN conductor is initially undetected, that situation will not persist continuously. If you have EV charging loads with the single-phase voltage monitoring open-PEN devices on all 3 phases, it is highly improbable that devices on all 3 phases will be "blinded" at the same time; in fact, the conditions are such that it's highly likely devices on two other phases will operate. This will change the phase balance very quickly, making it extremely likely that the remaining phase, on which OPDDs were originally "blinded" now see an "out of range" voltage in a relatively short time after the event.

    In a similar way, the operating characteristic of 30 mA RCDs is not guaranteed to protect children ... that doesn't mean we can't use them and they are useless - they offer more protection than not having the RCD., but they wont' protect 100 % of people 100 % of the time.

  • Thanks for reply, 

  • Thanks

  • the line to neutral voltages on all phases constantly change. So if the broken PEN conductor is initially undetected, that situation will not persist continuously.

    That would be more reassuring if these devices latched off once an out-of-bounds voltage had been detected - but as far as I can see there's no requirement for them to do that, indeed the need to recover after a "normal" power cut or brownout would be a temptation not to do so. Maybe the upcoming equipment standard will improve on that, but as far as I understand it, the devices are free to re-close as soon as the L-N voltage is back in bounds, even if the PE-Earth voltage is still hazardous.

    In mitigation, some models to include extra features to mitigate the risk further - e.g. c.p.c. current monitoring - but that's not universal.

       - Andy.

  • That would be more reassuring if these devices latched off once an out-of-bounds voltage had been detected - but as far as I can see there's no requirement for them to do that, indeed the need to recover after a "normal" power cut or brownout would be a temptation not to do so.

    BS 7671 doesn't at the moment is silent on auto-reset for any of the devices described in 722.411.4.1 (iii), (iv), or (v).

    Given the fact that in the same way L-N (or L-PE) voltages vary over time in broken neutral situations, so would the "PE to true Earth" voltage ... meaning that even if you were looking for the Neutral over 70 V to true Earth, it may (even in open PEN conditions) return to a voltage of below 70 V ... and auto-reset if that is enabled by the manufacturer.

    So, the same argument on auto-reset persists.

    One issue is that pretty much all conditions that can be monitored for open-PEN may be caused by something else ... which is why the old VOELCBs are no longer used (nuisance operation).

    In mitigation, some models to include extra features to mitigate the risk further - e.g. c.p.c. current monitoring - but that's not universal.

    Agreed.

  • meaning that even if you were looking for the Neutral over 70 V to true Earth, it may (even in open PEN conditions) return to a voltage of below 70 V ... and auto-reset if that is enabled by the manufacturer.

    So, the same argument on auto-reset persists.

    But in that case you're directly measuring the quantity you want to control - with the L-N proxy you're not - so with the latter is can re-close even though the PE-Earth is still hazardous at that moment.

    One issue is that pretty much all conditions that can be monitored for open-PEN may be caused by something else

    Indeed. Although time and patterns might give some clues. If the voltage drops off to near zero, remains flat, and then recovers to normal values (with only a little bounding around at each end) it's more likely to be a "normal" power cut, on the other hand if it continues to bounce around all over the place for many minutes, a broken N/PEN seems more likely. Overvoltages lasting more than a few seconds again might suggest a broken N too as faults on other phases should clear reasonably quickly. I guess there's no reason that self-closing devices can't continue to monitor the supply after they've disconnected the EV - and use that data to better inform the re-closing process.

       - Andy.

Reply
  • meaning that even if you were looking for the Neutral over 70 V to true Earth, it may (even in open PEN conditions) return to a voltage of below 70 V ... and auto-reset if that is enabled by the manufacturer.

    So, the same argument on auto-reset persists.

    But in that case you're directly measuring the quantity you want to control - with the L-N proxy you're not - so with the latter is can re-close even though the PE-Earth is still hazardous at that moment.

    One issue is that pretty much all conditions that can be monitored for open-PEN may be caused by something else

    Indeed. Although time and patterns might give some clues. If the voltage drops off to near zero, remains flat, and then recovers to normal values (with only a little bounding around at each end) it's more likely to be a "normal" power cut, on the other hand if it continues to bounce around all over the place for many minutes, a broken N/PEN seems more likely. Overvoltages lasting more than a few seconds again might suggest a broken N too as faults on other phases should clear reasonably quickly. I guess there's no reason that self-closing devices can't continue to monitor the supply after they've disconnected the EV - and use that data to better inform the re-closing process.

       - Andy.

Children
  • But in that case you're directly measuring the quantity you want to control - with the L-N proxy you're not - so with the latter is can re-close even though the PE-Earth is still hazardous at that moment.

    Granted, but that situation might only persist for a short time ... and also similarly if you are measuring 70 V to Earth, then things might look OK, and just after you reclose, the voltage rises again. Neither situation is 100 % ideal, but both provides some additional protection (at least in the from of an indication to the user) regarding a potentially hazardous occurrence that a report from HSL termed a "broadly tolerable" risk (specifically in domestic charging situations).

    Overvoltages lasting more than a few seconds again might suggest a broken N too as faults on other phases should clear reasonably quickly. I guess there's no reason that self-closing devices can't continue to monitor the supply after they've disconnected the EV - and use that data to better inform the re-closing process.

    In conceptual terms, this seems plausible. In terms of mandating this course of action, say in standards, what "rule of thumb" would (or could) be used for that?