Tea and sympathy or tough luck?
I always harbour a degree of empathy with contractors....been at the coal face myself for many years and I am well aware of the ups and downs.
However, I am not sure that I would warm the teapot and get the buns out in this case.
A contractor friend just completed 112 mid-range dwellings. He and the guys working for him are meticulously neat but far too nonchalant when it comes to regulatory requirements.
The site is complete, not one single EIC asked for or issued. That is until one of the last people to purchase one of the units was a contractor specialising in electrical I+T. That contractor identified the lack of certification and a number of concerning issues in his own home.
1. 16mm2 tails almost 15m in length supplied directly via an isolator from mains intake in the cubicle recessed in the exterior wall to a remote consumer unit. 100A service head fuse in each property (confirmed by NIE).
2. Cables enter the consumer unit from the rear without fire stopping. Timber frame house.
3. Ground floor ceilings peppered with downlights with a suggestion that this is unacceptable and
4. No certification issued and no inspection and testing carried out for any of the properties.
  • More specifically, a run of any length of 16mm2 PVC insulated and sheathed does not meet BS7671 when covered for overload by a 100A fuse
    Other thought, is there any downstream overload protection? I'm aware that "within spitting distance" the usual arrangement is for the CU incomer to be a 63A OPD (traditionally a Neozed bottle fuse, these days more likely a DP B63 MCB) - even the nature of the loads and/or combination of downstream MCBs might provide adequate defence against overloads.
  • true - and the D series  of those old bottle fuses as found in older  installations could safely break and limit a much higher PSSC than our BS1361/ BS88 offerings. The Germans (*) who engineered them were quite happy to consider that they can break 50kA AC or 8kA DC for the D3, a common incomer size.
    The 'newer' and slimmer Neozed are more likely 'only 16kA PSSC, and used to be the common fuse for house final circuits at a time we in the UK  were rewiring the old 3036s.
    Nowadays my friends abroad  indicate the incomer in the basement of a block or a large house is probably an NH type and that protects breakers per apartment or per floor and then MCBs per circuit.
    To be honest I'd support the addition of an incoming fuse in a UK CU as death or glory total energy limit, and also something you could take out and walk off with to ensure isolation.
    PS
    You know the designers are  German when
    *D style is a design invented in 1906 and initially called : "diametral abgesetzter zweiteiliger Edison-Schraubstöpsel" (affectionately "Diazed")  Since then other similar terms have been used with the same initial letters/.
    Diameter two step/two part Edison screwed fitting - well more or less. I'm not too sure if they mean there are two  parts, the fuse and the retaining cap, or the fuse has 2 diameters. The language sort of implies both really.
    The N series are "Neozed"
    neues  zweiteiliges Sicherungssystem mit Edisongewinde
    Same idea but 'new' two part fuse system - more compact, lower PSSC for CUs.
    * ref for the design date and early name is "Northern Bavarian Electrical Engineering" published in 1986 to celebrate 75 years of VDE standardisation.
    Foreign electrons look so different... Don't panic its a teaching board, not a live system.
  • Different ways of achieving the same objective!
  • No tea and no sympathy from me. An interview under caution and a prosecution. I sat in a Crown Court where a 23 year old woman died because testing had not taken place and the EIC was filled in in the site hut. I was listening to the pathologists  evidence of the injuries on the woman's body and looked at the effect it was having to the family having to listen to it. 42 new flats 42 fabricated test certificates.
    JP
  • What was the offence please, John? Gross negligence manslaughter? Fraud?
  • The charges were under Section 7 of the Health and Safety at Work Act. For the electricians mate the charge "failed to comply with section 7 in that  was that he failed to carry out an insulation resistance test. For the QS Section 7 failed to comply with Section 7 in that he failed to supervise.
    In a recent trial at Snaresbrook Crown Court with a young boy was killed in a pub garden the owner of the pub, an ex electrician was charged and convicted of manslaughter gross misconduct and got 9 years. The so called electrician got a not guilty on the manslaughter but got 2 years for the Health and Safety charge.
    I have given expert witness in 2 cases that have gone all the way to the Crown Court for fraudulent test certificates under a Trading standards offence  of issuing documentation by way of trade that is false or misleading. That offence is much easier to prove and caries an unlimited fine an/or 2 years imprisonment. Most cases I have done usually accept a caution or plead guilty in the magistrates court.
    JP
  • JP, am I right in saying that an IR test would not have detected the fault as it was line to the metal stud partition which then needed water to transport the potential to the apartment below?
  • Lyle
    Yes it would have done as the cable was sandwiched between the plasterboard and the metal stud work and for good measure a screw to secure the plasterboard passed through the cable between the line conductor and the CPC shorting them together. This would have been revealed if the required tests had been done in order. They were not done and the electricians mate confessed to this. The installation was energised and the CPC was blown away leaving the line conductor shorted to the MF studwork. The forensic science evidence was very interesting to hear. The cable and the screw were cut out of the wall intact and sent for examination.
    JP
  • John, thank you for sharing your expertise. Sadly, many tradesmen just want to get in and out as quickly as possible and move on to the next job. Fine for a painter and decorator, but not where safety comes into play.
    Do we have any idea whether there is a similar problem with gas fitters?
  • Absence of 30 mA RCD additional protection?