There are a group of shipping containers on a landfill site which has a PME supply. They have been converted into offices, a workshop and a canteen for use by a contractor carrying out groundwork’s on part of the site. There is a supply to a  3 phase distribution board in one of the containers to which the other containers are connected by plug and socket. There is a fence running alongside the containers, less than a metre away on which there are floodlights which are supplied from the same distribution board as the one supplying the container distribution board and a length of cable tray with armoured cables on it which go on to a couple of control panels mounted a few metres beyond the containers. BS 7671 prohibits PME generally for transportable buildings building with an exception where they are under the control of skilled or instructed persons. However converting to TT would mean having two earthing systems in touching distance. What is the best way to approach this?
each of the containers has a small DB in it with a Hager fuse holder as a main switch. Obviously these are not household premises, is this acceptable.