Rules on Spurs

Sorry in advance if this is a silly question, but I’m having a few issues with the electrics on an Air Conditioning install in England. The installation is on a domestic property and the house is very large which means that it’s incredibly impractical to run a new cable as the architects made sure to use all available space as living space so there are no voids or attics that can help us.

My question is, what is the maximum amount of power that we can take from  ring main that has no existing spurs on it please. I know we can have a 13a fused spur, but is there any way to get more than 13a without adding a new circuit please? The electrician is saying that 13a is the maximum, but I always thought that t was a little more. 

Parents Reply
  • Granted it will dissipate about 33% more power, but will the compressor be running non-stop even on a hot day?

    I am aware of 433.1.

    I see no reason why the ACU should not be connected by a 16 A MCB in a suitable enclosure, not elegant, but compliant!

Children
No Data