Sourcing electrical switchgear from online retailers

Sourcing electrical switchgear from online retailers but Chinese.

This is not meant to be a slur on foreign products.

I was looking at spd devices, as I may need to install a type 1 + 2 device. The costs of these is considerable, and when operating in the domestic sector, the passing of these costs to the customer often results in what is perceived to be an overpriced quote and the work is won by a less informed electrician who may happily install a type 2, unaware that the overhead supply cable may require a type 1.

In my research have seen devices that are far cheaper than the European counterparts but made in china. I have downloaded the datasheet for the device and seems to have the iec ratings and descriptions. The company is called Geya Electrical. What are the opinion on these products. Historically, China may have been produced low end manufacturing but are now turning out high end technologies...

Parents
  • China has been making e.g. iPhones for well over a decade, so as you point out, they can do high-end technology. I am not quite sure why a domestic install would need a Type 1 SPD.

  • I was surprised myself, but reading the pdf from surgedevices and conversation thereafter with them, the advice is that if the supply cable is from overhead cables and not underground cable than to install a type 1 +2 device. A property which may need a cu relocation due to an building extension has DNO cable attached to the external wall..a overhead supply....

    In such a case does a type 1+2 become necessary / appropriate?

    I believe that Chint which has a presence in the UK market is Chinese.

    I have also sent an email to Geya Electricals asking whether they have a European UK presence and if they OEM for any UK brands. See what they come back with???

Reply
  • I was surprised myself, but reading the pdf from surgedevices and conversation thereafter with them, the advice is that if the supply cable is from overhead cables and not underground cable than to install a type 1 +2 device. A property which may need a cu relocation due to an building extension has DNO cable attached to the external wall..a overhead supply....

    In such a case does a type 1+2 become necessary / appropriate?

    I believe that Chint which has a presence in the UK market is Chinese.

    I have also sent an email to Geya Electricals asking whether they have a European UK presence and if they OEM for any UK brands. See what they come back with???

Children
  • A property which may need a cu relocation due to an building extension has DNO cable attached to the external wall..a overhead supply....

    What sort of cable please? Bare wires on insulators, or ABC?

  • I am not sure...it's a black cable that is attached to the wall and supplies a row of properties...I guess abc cable...

    Would it affect the spd requirements?

  • To help you identify

    Aerial bundled Cable (ABC)actually looks like a bundle and is easily identified, because the twists and ties make it look bumpy - this is 3 phases and Neutral but single phase ABC would be just 2 individually insulated wires twisted.

    plain round is usually Concentric  which may be earthed concentric - for TNC-s

    or Split con allows N-E separation, and looks the same-ish from the outside but half the strands of the outer are insulated - Not always as clearly as this example,

    Split concnetric is ised on TNS or TNC-s on the load side of the NE split

    Mike

  • This is the photograph taken of the incoming cable attached to the external wall. As it is apparently not an underground supply cable, I assume it's an overhead supply cable. Therefore, a greater risk of lightning strike and type 1 +2 spd. 

    I do not have vast experience in this and would be happily guided by the forum Grinning 

  • Looks to me like it might be an "under eaves" supply - not commonly done these days, but lots about on older terraced properties. At some point the whole terrace will receive a supply - which can either be from overhead (i.e. cables hung from poles) or from underground with a "cut out" box on the outside of one of the properties - you might have to wander around to find it. Personally I'd consider how it arrives at the terrace to be the determining factor rather than how it enters your particular house (compare with a supply to a block of flats, with "sub main" cables to individual flats).

    That said, concentric cables run overhead are often considered to be equivalent to underground as the cable is self screening to some extent. ABCs are probably less vulnerable to having surges induced on then open wire (at least between conductors - which is probably what you're interested in if your have a TN system).

       - Andy.

  • Looks like a number (4) of concentric cables - presumably the fat one coming in on the left and the others, including the thin one bent round going out to the right to three consumers meters for different users. But that is a guess - we cannot really see.

    I think that is just junctions, and DNO the death or glory  fuses will be nearer the transformer, where ever that  is.

    Its also seems to be upside  down and at risk of getting water ingress via the cable entries. But that is an ecumenical   DNO matter.

    Mike.

    the thing that makes it overhead, is where the incoming supply comes from

    Is it something like this ?
    This image is 3 phase ABC pole to pole on top, and under that single phase ABCs to houses left and concetric to the right, and box of fuses or removable links pole-top. Oh and a bare stay wire (guy-line if you like)

  • That said, concentric cables run overhead are often considered to be equivalent to underground as the cable is self screening to some extent.

    In the surge protection world, we are also concerned about L-Earth and N-Earth.

    The Type 1 need, though, is about direct strike to overhead cable or pole-mounted transformer - more common with bare overhead, but can happen with insulated overheads especially pole-mounted transformer supply. By overheads to be clear I mean where there is a span (or catenary) between poles in the LV supply network to the property (or if looped as stated by Andy, nearby property).

    People will be quick to point out that 443 does not address direct strokes (and is not intended to). This is perfectly correct, but I would draw attention to 543.1 which does introduce direct strokes, and the first para says the section focuses "mainly on 443, but also can eb used in conjunction with BS EN 62305 or otherwise stated."

    In particular, though, with this issue, see NOTE to 534.4.1.1.

  • Thank you for the comments on the type of cable that may be supplying the property. I will investigate further. What seems to be the  / opinion with regards to whether a type 1 spd will be required? What are the guiding factors that will determine whether it will be Type 2 or a Type 1+2 device - could do with some guidance on this question. 

    Thanks 

  • What are the guiding factors that will determine whether it will be Type 2 or a Type 1+2 device - could do with some guidance on this question. 

    See NOTE to 534.4.1.1, and on top of that, "where required by BS EN 62305" for buildings with LPS (and therefore Section 443 of BS 7671 does not apply).

  • Which cable is the incomer (and which is the outgoer)? I don't like that cable which appears to have come adrift from its clips.