Energy let through Errors on Amtech/Trimble Selectivity Study Calculation

Hi, I'm just after a bit of advice on Energy let through Errors on the Amtech/Trimble Selectivity Study Calcualtion please. The error I keep seeing states:

The Energy let-through 60x10^3 of the protective device is greater than the Pre-Arc energy 50x10^3 for the upstream fuse.

Could anyone please explain:

1. What this is and why it could be an issue?

2. Does it make it a non-complaint design to BS7671, or is a non desirable but still acceptable issue?

3. And if its not compliant, why doesn't the software flag the error when you do the overall calculation, it only flags when you do a separate selectivity calculation?  

Thanks for any help.

Parents
    1. It is telling you that your upstream fuse may have started to operate before the downstream circuit breaker has fully cleared the fault under particular fault conditions. It is likely to continue so both fuse and circuit breaker will "trip"/"blow", i.e. you don't have a fully selective design (and even if it doesn't go, the fuse may well be preloaded and be more liable to let go on lower currents in future)
    2. Not necessarily if full selectivity is not a requirement specified by the Client. Indeed for some arrangements this may even be desirable (e.g. backup fuses)
    3. I presume because it would slow down the "normal" calculation, and not all designers are worried about selectivity (e.g. domestics and small commercials with tiers of MCBs...)
Reply
    1. It is telling you that your upstream fuse may have started to operate before the downstream circuit breaker has fully cleared the fault under particular fault conditions. It is likely to continue so both fuse and circuit breaker will "trip"/"blow", i.e. you don't have a fully selective design (and even if it doesn't go, the fuse may well be preloaded and be more liable to let go on lower currents in future)
    2. Not necessarily if full selectivity is not a requirement specified by the Client. Indeed for some arrangements this may even be desirable (e.g. backup fuses)
    3. I presume because it would slow down the "normal" calculation, and not all designers are worried about selectivity (e.g. domestics and small commercials with tiers of MCBs...)