Energy let through Errors on Amtech/Trimble Selectivity Study Calculation

Hi, I'm just after a bit of advice on Energy let through Errors on the Amtech/Trimble Selectivity Study Calcualtion please. The error I keep seeing states:

The Energy let-through 60x10^3 of the protective device is greater than the Pre-Arc energy 50x10^3 for the upstream fuse.

Could anyone please explain:

1. What this is and why it could be an issue?

2. Does it make it a non-complaint design to BS7671, or is a non desirable but still acceptable issue?

3. And if its not compliant, why doesn't the software flag the error when you do the overall calculation, it only flags when you do a separate selectivity calculation?  

Thanks for any help.

Parents
  • The Energy let-through 60x10^3 of the protective device is greater than the Pre-Arc energy 50x10^3 for the upstream fuse.

    To make sense of that you need to understand that pretty much all overcurrent protective devices can continue to let energy through even after they've started to open. Fuses will melt and create a gap in the fusewire, but they'll generate an arc which will let current continue to flow, until the gap in the fusewire gets large enough to quench the arc. Circuit breakers also have arcs to deal with but additionally have a finite time between de-latching and the contacts physically moving far enough apart to start interrupting the current as well. Plus there's manufacturing tolerances which mean you'd probably take a lower limit for the pre-arcing value and an upper limit for the total energy let-though. Once the device has started to open, it's "committed", and will almost certainly remain in the open (tripped, blown) state even if the current is interrupted somewhere else first.

    So too guarantee selectivity you need an upstream device that won't start to open given the maximum amount of energy the downstream device let though in total.

    As for compliance - that depends on the situation - whether its' required for safety or correct functioning of the installation. Sometimes it's just not practical to provide it for all circumstances (e.g. where backup protection is needed to deal with large PFCs) and sometimes (e.g where there are 30mA RCDs on a caravan supply and within the caravan) impossible to provide.

       - Andy.

  • Can't tell you how helpful this was, Andy. Thank you so much.